JS,

Great point about the air handler needing to be running.  Thanks.

 

 

From: greenbuilding-bounces at lists.bioenergylists.org
[mailto:greenbuilding-bounces at lists.bioenergylists.org] On Behalf Of John
Straube
Sent: Friday, February 25, 2011 11:17 AM
To: Green Building
Subject: Re: [Greenbuilding] ERV's and air handlers

 

It is effective and practical to use the air handlers and ductwork to
distribute air. It is quite reasonable to inject the fresh air on the return
side of the AHU and not uncommon,

Two challenges with the approach.  If you inject the air into the ductwork,
the AHU would need to be running to distribute the air.  It is rare that the
low ventilation air flows will move properly through ducts designed for
heating/cooling.  We have solved this my using a FanCycler control (google
it) so that the ERV runs on a duty cycle to deliver air, and triggers the
AHU to run on low speed if needed.

Second issue, is where the exhaust air comes from.  A good solution if the
duct run is not long, is to exhaust from the bathroom, but any hallway or
open space is also OK. 

I dont know what the LR return duct is. 

 

On 2011-02-25, at 10:29 AM, J Messerschmidt wrote:





Since you are all talking about ERV's, I thought I'd ask a question.  The
(conventional) mechanical engineer of a house I'm currently building didn't
have an ERV spec'd.  Since I'm tightening it up, I recommended one so he
added it to one of three air handlers. 

 

I see on the plans that there is a direct duct coming from the outside into
the ERV and then into the air handler.  Another duct leads from a LR return
duct to the ERV and then to the outside.  Disregarding the fact that this is
on only one of the units, it is an effective solution to go through the air
handlers?  If so, then should I lobby to add it to the other units?

 

John

 

 

 

From: greenbuilding-bounces at lists.bioenergylists.org
[mailto:greenbuilding-bounces at lists.bioenergylists.org] On Behalf Of David
Posada
Sent: Tuesday, February 22, 2011 1:30 PM
To: 'Tedd Weyman'
Cc: greenbuilding at lists.bioenergylists.org
Subject: Re: [Greenbuilding] ERV's

 

Hi Tedd,

Thanks for your input. You raise a good point about the wind pressure from
the local microclimate - something to consider.

 

Since ASHRAE 62.2 is trying to prevent to under-the-door infiltration of air
quality issues you mention, and if the units have their own make-up air
supply you could probably use door sweeps. You're right - either the bath
fan or the stove hood exhaust alone could ventilate the unit in exhaust-only
mode, so the question then becomes where to get the make-up air supply?

 

Options seem to fall into two camps - local, individual make-up air at the
outer wall from a trickle vent or spot ERV, or else a central system ducted
from the corridor.

 

For local make-up air, one might ask if the trickle vent raises questions of
thermal comfort and/ or additional heat load from unconditioned outside air,
and if the Spot ERV is thus a good alternative to help condition that
make-up air. Other options might be based around centrally supplied make-up
air, so to inform the cost-benefit comparisons it's great to hear input like
yours.  

 

David

 

 

From: Tedd Weyman [mailto:weyman_tedd at yahoo.com] 
Sent: Tuesday, February 22, 2011 7:10 AM
To: David Posada
Cc: greenbuilding at lists.bioenergylists.org
Subject: ERV's

 

I recently decided against using a spot ERV for a 5 room, 1200' sq cottage
(radiant heat) because the local wind pressures and stack effects make the
pressure drives on the exterior just too overwhelming for a light weight,
low-CFM, ERV. If your heat recovery and air exchange are not from a central
system (i.e. powerful enough to take over the buildings climate, including
ducting to all rooms), its unlikely a small ERV will be able to overcome the
external environmental forces on the building your describing (i.e small
apartments or condos).

 

A normal kitchen exhaust (if its externally vented and not just an internal
filter - has 400 to 1000 CFM) and your bathroom exhaust (120+ CFM) are more
(locally) powerful than a full sized, let alone a spot ERV and probably
perfectly adequate to meet all the air exchange needs in small and medium
sized living units. Timer controlled fresh air supply might be needed to
complement/supplement the exhaust of a timed bathroom exhaust and during the
cooking cycles of the kitchen exhaust.  Your under-door fresh air supply
(allegedly fresh air) will defeat the spot HRV's performance (its not just a
question of volume of air per minute, its the flow rate and pressures).

 

If you live in a apt/condo, under-the-door positive pressure from the
hallway brings is ugly.  Give me independent air such as the trickle-vent or
a coordinated (with exhaust) timed fresh air supply any day over the stale
smells and particulates of fried fish, cigarettes, cat hair and marijuana
smoke from the neighbours. 

 

I bet there are half a dozen other things you can do per unit for the same
price (investment) as the spot ERV that will more constructively affect
living climate, improve the air quality, and conserve/recycle/reduce energy
waste.

 

TW

 

 

 

 

 

 

 

_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
Greenbuilding at bioenergylists.org

to UNSUBSCRIBE or Change your List Settings use the web page
http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioener
gylists.org

 

Dr John Straube, P.Eng.

Associate Professor

University of Waterloo

Dept of Civil Eng. & School of Architecture

www.buildingscience.com

 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.bioenergylists.org/pipermail/greenbuilding_lists.bioenergylists.org/attachments/20110225/c72265e3/attachment.html>


More information about the Greenbuilding mailing list