[Greenbuilding] Commercial Water Heaters
Peter Kidd
peterkidd at shaw.ca
Tue Jul 17 07:22:19 CDT 2012
great example of re-commissioning. that said, is the building
electrically heated, and with that low a hot water demand, are they
likely to see that reduction in coincident demand?
> My firm just wrapped up a lighting retrofit at a local municipal
> building where, as best as I can tell, there are four high capacity
> electric water heaters. The two shown in this first picture
> (http://i362.photobucket.com/albums/oo69/HereinHalifax/Img_1547.jpg)
> each draw 36.0 kW and the remaining two (one of which is shown here:
> http://i362.photobucket.com/albums/oo69/HereinHalifax/Img_1550.jpg)
> are rated at 18.0 kW. Thus, the combined load of these four tanks is
> 108.0 kW.
>
> These tanks are used almost exclusively for hand washing purposes, and
> so we will be disconnecting all three top elements in the two 36.0 kW
> tanks, as well as two of the three bottom elements, effectively
> de-rating each tank to 6.0 kW. As you can see in the first
> photograph, the two tanks feed a common supply, and 12.0 kW combined
> with almost 1,000 litres of storage capacity is more than sufficient
> to meet all of their requirements. The two remaining tanks likewise
> serve mostly hand washing needs and will be de-rated to 6.0 kW as
> well; with that, the total connected load falls to 24.0 kW, for a net
> savings of 84.0 kW.
>
> In terms of cost savings, an 84.0 kW reduction in coincident demand
> will reduce our client's demand charges by $9,350.21 a year, i.e.,
> 84.0 kW x $9.276 per kW, per month x 12 months/year. It will also
> shift some 16,800 kWh of energy each month to Nova Scotia Power's
> lower cost second tier, for an additional savings of $5,842.37 a year,
> i.e., 84.0 kW x 200 kWh/month, per kW x ($0.09904 - $0.07006 per kWh)
> x 12 months/year. Taken together, this represents a savings of over
> $15,000.00 a year, at current rates, achievable with no discernible
> loss in water heater performance.
>
> By simply reducing the power draw of these tanks, we will save our
> client more money each year than by upgrading the facility's entire
> lighting system, and will have done so at effectively zero cost (their
> lighting retrofit will reduce coincident demand by an estimated 37.7
> kW, and de-rating their water heaters will more than triple that).
> Five to ten minutes is all that's required to remove the jumper wires
> that connect the terminal block to each corresponding heating element.
>
> We've de-rated dozens of similarly oversized water heaters over the
> years and in many cases implemented timer controls to lock-out their
> operation during normal business hours, thereby reducing the
> customer's peak demand even further; thankfully, there have been no
> complaints of hot water run-out to date, and so the results have
> proven more than satisfactory. This particular building initially
> served as a police station, and so these water heaters originally feed
> a bank of showers; the building was subsequently converted to general
> offices and, consequently, their DHW usage is vastly lower.
>
> The other thing we like to do is run the circulator pumps on
> multi-program timers so that they operate only as required. For
> example, we may run a circulator pump a couple hours at the start of
> each weekday morning, shut it off, then turn it back on for an hour or
> so mid-day and perhaps another hour later in the day. In most cases,
> we can limit the operation of a pump to twenty or twenty-five hours a
> week, as opposed to one hundred and sixty-eight; after all, there's
> really no need to push hot water through an extensive network of pipes
> at 02h00 or 03h00 in the morning (with all the inherent losses), when
> the last person had left the building eight hours prior.
>
> BTW, you can view one of the rooms that we had upgraded at:
> http://i362.photobucket.com/albums/oo69/HereinHalifax/Img_1546.jpg.
> Here, we replaced 3-lamp F34T12 prismatic troffers that consumed
> 130-watts each with 2-lamp 28-watt 850 series T8 troffers that draw
> just 42-watts, for a two-thirds reduction in demand. Amazingly, light
> levels in this area increased two and a half to three fold
> (originally, 14 to 17 foot candles, now 43 to 46 foot candles). Far
> more light and much better light quality, with fewer watts to boot.
>
> Cheers,
> Paul
>
> _______________________________________________
> Greenbuilding mailing list
> to Send a Message to the list, use the email address
> Greenbuilding at bioenergylists.org
>
> to UNSUBSCRIBE or Change your List Settings use the web page
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>
More information about the Greenbuilding
mailing list