[Greenbuilding] Visible Flames (Fireplaces) in Tight Houses
Norbert Senf
norbert.senf at gmail.com
Wed Dec 3 18:18:12 CST 2014
Masonry chimneys require 2" clearance to combustibles. Clearance, as in
"air space".
1" on an exterior wall, depending on local codes.
This all does raise issues about how you do envelope penetrations in low
energy houses.
A masonry chimney is obviously a thermal bridge, not to mention how do you
attach a vapor barrier?
With metal chimneys, the only thing I have come across so far is an
insulated cathedral ceiling support, made for ICC Excel chimney.
It uses insulation instead of an air space, and has been tested and listed
to the ULC-621 standard.
On Wed, Dec 3, 2014 at 6:48 PM, Clarke Olsen <colsen at fairpoint.net> wrote:
> So.. insulating the space in masonry chimney should be ok? I'm with you on
> the offset - I want to look up an see that sunshine at the end of the
> chimney.
> Clarke Olsen
> clarkeolsendesign.com
> 373 route 203
> Spencertown, NY 12165
> USA
> 518-392-4640
> colsen at taconic.net
>
>
>
>
> On Dec 3, 2014, at 2:59 PM, Frank Tettemer <frank at livingsol.com> wrote:
>
> > Clarke and Eli,
> >
> > I need to say that I'm extremely alarmed by the idea of filling that 2"
> space with vermiculite, Roxul, or Fiberglass insulation. Especially with in
> a chase. The rise in temperature of the steel components of the chimney,
> due to the insulation surrounding them, would exceed safe levels. The
> chimney could fail.
> >
> > I also would like to add a note that, although acceptable by code,
> planning an insulated chimney with off-sets, (45 or 90 degree) is also not
> a good idea. Off sets are an area that create 'eddy currents' within the
> chimney, and thus create cooler and hotter areas within the chimney liner.
> These eddy currents can also create landings for creosote deposits. This
> causes wear and tear on the steel components, and that is not desirable.
> >
> > Off sets need additional structural support, to prevent the lower
> portion of the chimney from bearing the weight and load of the upper
> portion of the chimney. I have seen a situation where these components were
> not structurally supported. The weight of the upper portion of the chimney
> levered the 45 degree parts to open up, and allow a fire to start.
> >
> > Off sets with in a chase also need to be surrounded by a tightly
> constructed heat shield. This is difficult to do well, and if it can't be
> done well, it needn't be done at all. Careful planning and design, so thata
> straight chimney can be installed is not mandatory; but it is the only
> acceptable idea to consider. What could possibly trump fire safety?
> Certainly not aesthetics, and certainly not budget.
> >
> > Sorry for my Rant, Rant, Rant. I've witnessed too many house fires, of
> friends and neighbours, to be complacent.
> > I'm apologetic for my rant, but firm about fire safety,
> >
> > --
> > Frank Tettemer
> > Living Sol ~ Building and Design
> > www.livingsol.com
> > 613 756 3884
> >
> >
> > On 03/12/2014 2:32 PM, Clarke Olsen wrote:
> >> What is the reason for not insulating that space? Why would vermiculite
> be a better conductor than air?
> >> Does this apply to metal and masonry chimneys?
> >> Clarke Olsen
> >> clarkeolsendesign.com <http://clarkeolsendesign.com>
> >> 373 route 203
> >> Spencertown, NY 12165
> >> USA
> >> 518-392-4640
> >> colsen at taconic.net
> >>
> >>
> >>
> >>
> >> On Dec 3, 2014, at 11:14 AM, Norbert Senf <norbert.senf at gmail.com
> <mailto:norbert.senf at gmail.com>> wrote:
> >>
> >>> Under no circumstances should anything be put into the 2" air space
> that is specified around a UL/ULC listed factory chimney.
> >>>
> >>> If you put vermiculite in there, you are voiding the UL listing of the
> chimney by virtue of not installing according to "manufacturers
> instructions". This creates liability for you.
> >>>
> >>> This is a common misconception, and is the reason for the "attic
> radiation shield" required in attics, which are required to have a storm
> collar on them, specifically to prevent people from putting insulation into
> the 2" air space. Here in Canada, a radiation shield is also required
> around chimneys in chases, specifically to avoid this scenario.
> >>>
> >>> This is not an issue in normal use. However, the ULC-621 listing means
> the chimney system (including the air space) has been tested to survive
> three 30 minute chimney fires at 2100F, without torching the adjacent
> walls. Put vermiculite into the air space, and the wall will burn. I have
> seen photos of where this has happened.
> >>>
> >>> Norbert
> >>>
> >>> On Wed, Dec 3, 2014 at 9:43 AM, <conservationarchitect at rockbridge.net
> <mailto:conservationarchitect at rockbridge.net>> wrote:
> >>>
> >>> Alan
> >>> How tight were the openings into this closed loop fireplace?
> This may be acceptable to my client. .6ach at 50pa
> >>> <mailto:.6ach at 50pa>is impressive with these handicaps. What
> >>> would your recommendation for interior cloths dryer be?
> >>> As an alternative to the insulated chase, could you define a
> >>> space up to a triple wall chimney that has the specified
> >>> clearance to combustible material filled with non combustible
> >>> insulation such as vermiculite.
> >>> Thanks
> >>> Eli
> >>>
> >>> _______________________________________________
> >>> Greenbuilding mailing list
> >>> to Send a Message to the list, use the email address
> >>> Greenbuilding at bioenergylists.org <mailto:
> Greenbuilding at bioenergylists.org>
> >>>
> >>> to UNSUBSCRIBE or Change your List Settings use the web page
> >>>
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> >>
> >>
> >>
> >> _______________________________________________
> >> Greenbuilding mailing list
> >> to Send a Message to the list, use the email address
> >> Greenbuilding at bioenergylists.org
> >>
> >> to UNSUBSCRIBE or Change your List Settings use the web page
> >>
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> >
> >
> > _______________________________________________
> > Greenbuilding mailing list
> > to Send a Message to the list, use the email address
> > Greenbuilding at bioenergylists.org
> >
> > to UNSUBSCRIBE or Change your List Settings use the web page
> >
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> >
>
>
>
> _______________________________________________
> Greenbuilding mailing list
> to Send a Message to the list, use the email address
> Greenbuilding at bioenergylists.org
>
> to UNSUBSCRIBE or Change your List Settings use the web page
>
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>
--
Norbert Senf
Masonry Stove Builders
25 Brouse Road, RR 5
Shawville Québec J0X 2Y0
819.647.5092
www.heatkit.com