The above sounds very much like a double-stud wall section so one should
choose which of the two frame walls is load-bearing .
Logically, the interior wall would be the one designated as load-bearing
even if only because doing so shortens the spans of flexural members like
joists and rafters. When we're talking about fat superinsulated walls, the
difference in span can mean a difference in one joist size.
In making the interior wall loadbearing, there's no need for the exterior
wall to be a 2x6 OVE stud wall -- it can be a 2x3 or 2x4 wall with studs
at 24" o/c, single top plates, no lintels over openings (assuming that
we're talking about low-rise residential building)
One just needs to ensure that one allows for eventual shrinkage of
cross-grain framing members (ie sill & top plates, rim joists, lintels) in
the bearing wall so that the curtain wall does not inadvertantly become
loadbearing.
--
=== * ===