Regardless of the permeability of the foam, the asphalt shingles or metal roofing finish are almost perfect vapor barrier.
Unvented cathedral ceilings always have to dry to the inside.
Closed-cell foam insulation makes sure the water vapor never gets to the sheathing by diffusion or air leakage in the first place.

> On Feb 20, 2017, at 12:24 PM, Topher Belknap <topher at greenfret.com> wrote:
> 
> 
> Greetings,
> 
> What is the permeability of the spray foam?  If it is low, you will need
> to ensure drying to the inside, which seems problematic.  Have you run a
> WUFI simulation, or similar?
> 
> Thank you kindly,
> 
> Topher
> 
> -- 
> Topher Belknap
> Green Fret Consulting
> Kermit didn't know the half of it...
> http://www.GreenFret.com/
> (207) 882-7652
> 
> On 2/19/2017 11:24 PM, Sacie Lambertson wrote:
>> We're in Zone 4.  We will put in several inches of sprayed foam
>> immediately under the roof; sealed to the tops of existing walls.  Blown
>> in cellulose is the next layer.  Area/attic is _not_ ventilated.  The
>> house will be tight.
>> 
>> Will have an HRV system as well.
>> 
>> Should have described whole plan to begin with.  Again, appreciate the
>> comments.
>> 
>> Sacie
>> 
>> On Sun, Feb 19, 2017 at 9:16 PM, John Straube <jfstraube at uwaterloo.ca
>> <mailto:jfstraube at uwaterloo.ca>> wrote:
>> 
>>    There are numerous reasons to ventilate attics and cathedral
>>    ceilings: removal of moisture is the most important.
>>    Another reason is to limit ice damming in climates with sufficient
>>    snow and weather that cycles near to freezing temperatures. If you
>>    insulate enough, you dont need to ventilate for that reason.
>>    BUT, there is no way you can build cathedral ceilings with cellulose
>>    and NOT ventilate without taking serious risks.  Some cellulose
>>    companies have been selling this idea for years, and we (and most
>>    other forensic consultants) have seen sufficient failures to realize
>>    that it is too risky in most cases.  If the house below is super air
>>    leaky and hence very dry in cold weather you can often “get away
>>    with it” but modern houses in cold climates with higher RH levels
>>    (e.g. not 15%!) cannot tolerate small air leaks.
>>    Do a great job of air sealing, live in a climate that is not too
>>    cold (e.g. Zone 3 or 4) and you might be able to pull off a
>>    cellulose unvented cathedral. Still risky, but must less so.
>>    An alternate design is to put enough insulation outboard of the
>>    sheathing and cellulose. This is a good retrofit option. Fill up the
>>    available rafter space, then put an air barrier membrane on the
>>    sheathing, and add sufficient R-value on the exterior to avoid
>>    condensation (this amount varies ratiometrically with the amount of
>>    cellulose R-value, the outdoor climate, and the indoor winter humidity.
>> 
>>    PS I have R-100 in my house… roughly.  about 28” of cellulose in a
>>    flat ceiling under a well-ventilated attic. No furring, just 2x4
>>    bottom chords of trusses supporting 1/2” GWB with standard screw
>>    patterns. R-100 does not make a lot of sense, until you see the
>>    price difference between R-60 and R-100 is so small
>>    But Frank’s experience is worth a lot…. 30 houses over more than a
>>    decade.  That is worth more than any experiment in my books.
>> 
>> 
>>> On Feb 19, 2017, at 9:32 PM, Reuben Deumling <9watts at gmail.com
>>    <mailto:9watts at gmail.com>> wrote:
>>> 
>>> R80, huh? Wow.
>>> I'm curious, Frank, what you make of the article circulated here
>>    recently that suggested that (and I'm paraphrasing) above R30 the
>>    ventilation of cathedral ceilings could be skipped?
>>> 
>>> On Sun, Feb 19, 2017 at 6:05 PM, Frank Tettemer
>>    <frank at livingsol.com <mailto:frank at livingsol.com>> wrote:
>>> I agree with David's suggestion, to alleviate concern,
>>> However, for over a decde we have in 22 inches of blown in place
>>    cellulose = (R-80?). this had held up consistantly each year, We put
>>    up MemBrain by Certainteed stapled to the ceiling joists @ 24" o.c..
>>> Then, 1x4 spruce strapping on 12" o.c.
>>> 
>>> Then 1/2" drywall, double screwes into 1x4 on 9" o.c..
>>> 
>>> At least 30 ceilings and insulation installations over 14 years,
>>> with no failures except in my own garage ceiling where I stepped
>>    off the joists with my big bad foot.
>>> 
>>> Question?: Do you have a plan to block off the vented soffits, and
>>    allow ventilation channels from the vented soffit, above the
>>    cellulose, to the vented ridge, or, maximum vent box, or similar?
>>> More opportunities and good use of corrugated cardboard?
>>> Or inexpensive Moore vent/rafter vents, and vertical cardboad
>>    baffles, from outside face of the wall plate, up to the rafter vents?
>>> 
>>> Cheers,
>>> Frank Tettemer
>>> 
>>> On 2017-02-18 12:29 PM, David Wentling via Greenbuilding wrote:
>>> _______________________________________________
>>> Greenbuilding mailing list
>>> to Send a Message to the list, use the email address
>>> Greenbuilding at bioenergylists.org
>>    <mailto:Greenbuilding at bioenergylists.org>
>>> 
>>> to UNSUBSCRIBE or Change your List Settings use the web page
>>> 
>>    http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>>    <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>>> 
>>> 
>>> _______________________________________________
>>> Greenbuilding mailing list
>>> to Send a Message to the list, use the email address
>>> Greenbuilding at bioenergylists.org
>>    <mailto:Greenbuilding at bioenergylists.org>
>>> 
>>> to UNSUBSCRIBE or Change your List Settings use the web page
>>> 
>>    http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>>    <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>>> 
>>> _______________________________________________
>>> Greenbuilding mailing list
>>> to Send a Message to the list, use the email address
>>> Greenbuilding at bioenergylists.org
>>    <mailto:Greenbuilding at bioenergylists.org>
>>> 
>>> to UNSUBSCRIBE or Change your List Settings use the web page
>>> 
>>    http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>>    <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>> 
>>    Dr John F Straube, P.Eng.
>>    jfstraube at uwaterloo.ca <mailto:jfstraube at uwaterloo.ca>
>>    www.JohnStraube.com <http://www.JohnStraube.com>
>> 
>> 
>> 
>> 
>>    _______________________________________________
>>    Greenbuilding mailing list
>>    to Send a Message to the list, use the email address
>>    Greenbuilding at bioenergylists.org
>>    <mailto:Greenbuilding at bioenergylists.org>
>> 
>>    to UNSUBSCRIBE or Change your List Settings use the web page
>>    http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>>    <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>> 
>> 
>> 
>> 
>> _______________________________________________
>> Greenbuilding mailing list
>> to Send a Message to the list, use the email address
>> Greenbuilding at bioenergylists.org
>> 
>> to UNSUBSCRIBE or Change your List Settings use the web page
>> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>> 
> 
> _______________________________________________
> Greenbuilding mailing list
> to Send a Message to the list, use the email address
> Greenbuilding at bioenergylists.org
> 
> to UNSUBSCRIBE or Change your List Settings use the web page
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org





More information about the Greenbuilding mailing list