<br><br>---------- Forwarded message ----------<br>From: "John Straube" <<a href="mailto:john@buildingscience.com">john@buildingscience.com</a>><br>To: "elitalking" <<a href="mailto:elitalking@rockbridge.net">elitalking@rockbridge.net</a>>,        <a href="mailto:greenbuilding-bounces@lists.bioenergylists.org">greenbuilding-bounces@lists.bioenergylists.org</a>,        "John O'Brien" <<a href="mailto:john@boardom.ca">john@boardom.ca</a>><br>
Date: Mon, 25 Oct 2010 12:54:56 +0000<br>Subject: Re: [Greenbuilding] ERV strategy<br>Short answer again.<br>
ERVs do not dehumidify. The reduce the load on the dehumidifier when and only when it is lower RH indoors than a outdoors.<br>
<br>
John Straube<br>
519 741 7920<br>
Sent via BlackBerry<br>
<br>
<br>
-----Original Message-----<br>
From: "elitalking" <<a href="mailto:elitalking@rockbridge.net">elitalking@rockbridge.net</a>><br>
Sender: <a href="mailto:greenbuilding-bounces@lists.bioenergylists.org">greenbuilding-bounces@lists.bioenergylists.org</a><br>
Date: Mon, 25 Oct 2010 08:41:47<br>
To: John O'Brien<<a href="mailto:john@boardom.ca">john@boardom.ca</a>><br>
Cc: <<a href="mailto:satjiwan@alumni.brandeis.edu">satjiwan@alumni.brandeis.edu</a>>; listserv Green Building new<<a href="mailto:greenbuilding@lists.bioenergylists.org">greenbuilding@lists.bioenergylists.org</a>><br>

Subject: Re: [Greenbuilding] ERV strategy<br>
<br>
John, thanks for responding to my question.<br>
<br>
<br>
<br>
Using your example, you must have another process to lower the humidity<br>
indoors in order to preserve that dryness with ERV.  Night flushing during<br>
fair weather summer days here in Virginia Mountains, brings in cool humid<br>
air.  When it is 95F outside, 75F inside still feels much better, even if at<br>
70% humidity.  Less humidity would be better.  The outdoor air later in day<br>
is just as humid in absolute terms (#vapor/unit volume).  Please correct me<br>
if I am wrong, however, in your example of the same temp but with the same<br>
relative humidity, the ERV has no dehumidifying ability. The indoor air must<br>
be dryer in order to preserve that dryness.<br>
<br>
<br>
John O'Brien writes:<br>
You seem to be making the issue more complex than it needs to be I<br>
think. Assume both inside and outside temperatures are the same. You<br>
have nicely dehumidified all your nice inside air to lets say a bone<br>
chilling dry 20%, while outside it's raging ontario swamp heat wave at<br>
100%.<br>
<br>
With an HRV you're exchanging 20C air with 20C air... Check. HRV is<br>
done. You've just replaced X amount of dry air with X amount of 100%<br>
humidity air.<br>
<br>
With your ERV, you've exchanged 20C air with 20C air again, but you've<br>
also transferred your 20% in_humid with your 100% out_humid, which I<br>
will assume will give you a new entering humidity of something in the<br>
middle.. Let's say 60%. You now have 40% less humidity to remove.<br>
<br>
Numbers don't make sense, but the concept is correct if not very<br>
simplistic. I think what Steve was talking about was with regards to<br>
exhausting 100% humid bathroom/shower air, with the ERV you're<br>
actually recyling some of that moisture back into the house. I imagine<br>
the next SUPER_RV will have humidity sensors to disable exchange<br>
depending on interior and exterior flow conditions.<br>
<br>
j<br>
<br>
<br>
<br>
<br>
<br>
_______________________________________________<br>
Greenbuilding mailing list<br>
to Send a Message to the list, use the email address<br>
<a href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><br>
<br>
to UNSUBSCRIBE or Change your List Settings use the web page<br>
<a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a><br>
<br>
<br></div><br><div style="visibility: hidden; left: -5000px;" id="avg_ls_inline_popup"></div><style type="text/css">#avg_ls_inline_popup{position: absolute;z-index: 9999;padding: 0px 0px;margin-left: 0px;margin-top: 0px;overflow: hidden;word-wrap: break-word;color: black;font-size: 10px;text-align: left;line-height: 130%;}</style>