    <font face="Helvetica, Arial, sans-serif">You cant use a normal
      on-off thermostat with a modulating control.  <br>
      The simplest thermostat for use with an SCR or TRIAC would have
      what is called proportional control.<br>
      For example, if the temperature fell below 68F by 0.1 F, 100W
      would be delivered to the heater, of the temperature dropped to
      67.8F, 200W would be provided and if it dropped to 67F, 1000W
      would be delivered.<br>
      Because a smaller amount of heat is added with small temperature
      drops, the temperature does not oscilate as much as an on-off
      control with a 3F deadband as described in the example.<br>
      More sophisticated thermostats use proportional-integral controls
      or proportional-integral-derivate controls (PID) which I wont go
      into.  Suffice it to say, we can control the temperature at the
      thermostat to better than +/-0.1F with a PID thermostat control
      and an SCR in our lab setups.<br>
      <br>
      You are correct that a relay and a thermostat with a tight dead
      band (dead band= temperature difference between when the
      thermostat turns on and off) can result in pretty good control if
      the heating device does not have a lot of thermal mass (like an
      electric baseboard!).<br>
      In an experiment in my own house, I used a "simple" on-off
      temperature control with a 0.1F deadband to control air
      temperature to +/-0.2F simply by having the heater turn on for as
      little as 10 seconds and then off again when the sensed
      temperature rose 0.1F.<br>
      As you state, all you need is a durable relay.  It is often easier
      to use an SCR or Triac than it is to get a relay that will durably
      (e.g. 10 million cycles before failure) control large electric
      flows.  For tight temperature control and larger heaters (eg e.g.
      0.1 F and 1500W), a modulating control is the more common
      solution.  For smaller loads (100W?) and broad temperature ranges
      (0.5F) solid state relays tend to be better. For very small
      electric loads (10W or less), SSR (solid state relay) technology
      is routinely used.<br>
      <br>
      <br>
    </font>
    <pre class="moz-signature" cols="0">Dr John Straube, P.Eng.
<a class="moz-txt-link-abbreviated" href="http://www.BuildingScience.com">www.BuildingScience.com</a></pre>
    <br>
    On 11-12-19 2:09 PM, Corwyn wrote:
    <blockquote cite="mid:4EEF8C03.7080308@midcoast.com" type="cite">On
      12/19/2011 9:28 AM, John Straube wrote:
      <br>
      <br>
      <blockquote type="cite">So, for example, a baseboard of 1500W
        output may turn on for 10 minutes,
        <br>
        then turn off and the room cools down for 20 minutes, and then
        the cycle
        <br>
        repeats. The temperature falls to, say, 68F, the heater turns
        on, the
        <br>
        temperatures rises over the ten minutes to, say, 71 F, and the
        switches
        <br>
        off again.
        <br>
        With a a modulating control like a Triac, a very smart
        thermostat would
        <br>
        attempt to adjust the output of the heater to 500W continuously
        (because
        <br>
        500 Watts for 30 minutes delivers the same energy as 1500W for
        10
        <br>
        minutes every 30 minutes). This means the average current is
        lower, the
        <br>
        electric heater runs at a lower temperature, and the room
        temperature
        <br>
        stays more constant.
        <br>
      </blockquote>
      <br>
      This sounds great on paper (phosphors), but I don't see how it
      helps in real life.  If your thermostat is only accurate to 1.5
      degrees (hysteresis of 3 degrees as you baseboard example) then
      the temperature is going to rise until it reaches 71 and then
      adjust; same as the full bore baseboard.  It is not like it KNOWS
      it will need 500W in advance.
      <br>
      <br>
      If the thermostat is more accurate, then you might as well use it
      on the full bore (presumably cheaper) baseboard.  With a really
      accurate thermostat, you could probably get down to 1 minute on
      out 3.  Does anyone really think that isn't good enough?  That
      they need modulation by the second?  That the thermal mass of a
      baseboard heater even responds that quickly?
      <br>
      <br>
      I guess there could be an advantage of using a triac over a relay
      if the MTBF is significantly longer (more cycles).  Is that the
      case?
      <br>
      <br>
      <br>
      Thank You Kindly,
      <br>
      <br>
      Corwyn
      <br>
      <br>