Stuart I love that solution. I have heard rumors of this being done but never heard anyone who succeeded. Getting the cfm high enough while still keeping the system balanced was a real obstacle.<div><br clear="all">Gennaro Brooks-Church<br>
Director, Eco Brooklyn Inc.<br>Cell: 1 347 244 3016 USA<br><a href="http://www.EcoBrooklyn.com" target="_blank">www.EcoBrooklyn.com</a><br>22 2nd St; Brooklyn, NY 11231<br><br>
<br><br><div class="gmail_quote">On Thu, Mar 22, 2012 at 3:54 PM, Stuart Fix <span dir="ltr"><<a href="mailto:sfix@renubuildings.com">sfix@renubuildings.com</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
Hi Alan,<br>
<br>
Check out the Mitsubishi Mr. Slim series. They go down to 9000 Btu/h, and<br>
can operate to -20C. We've built a prototype that uses their ducted<br>
fancoil unit inline with the ERV supply, with the addition of a return air<br>
duct to feed the extra CFM.<br>
<br>
So in operation:<br>
<br>
- ERV operates continuously, 100-200CFM, blowing through the fancoil (must<br>
use extremely efficient ERV for this to make sense, try UltimateAir<br>
RecoupAerator)<br>
<br>
- Fancoil kicks on as heating or cooling requires, using the 100-200CFM of<br>
the ERV and sucks an additional  300-500 CFM through the return air duct.<br>
Using the RecoupAerator makes this easy, as its ECM motors are self<br>
balancing, so it'll compensate as the Fancoil depressurizes the system.<br>
<br>
In addition, if your climate is cold enough to require it, the Mitsubishi<br>
makes a PAC controller that lets you use the fancoil with an inline<br>
electric heater even when the condensing unit outside has locked out due<br>
to cold weather.<br>
<br>
You'll end up upsizing the supply trunk to around 10", but that's still<br>
small enough for the ERV to handle by itself.<br>
<br>
This may not have made sense, drop me a line if you'd like more info or a<br>
sketch.<br>
<br>
Cheers,<br>
<br>
Stuart Fix, P.Eng., LEEDŽ AP<br>
PHI Certified Passive House Designer<br>
MASc. Building Science<br>
Mechanical Engineer<br>
ReNü Building Science Inc.<br>
<br>
#206, 506B St. Albert Trail | St. Albert, Alberta | T8N 5Z1 | C.<br>
<a href="tel:780.554.8192" value="+17805548192">780.554.8192</a> | <a href="mailto:sfix@renubuildings.com">sfix@renubuildings.com</a><br>
<br>
<br>
Message: 1<br>
Date: Thu, 22 Mar 2012 11:43:26 -0400<br>
From: Alan Abrams <<a href="mailto:alan@abramsdesignbuild.com">alan@abramsdesignbuild.com</a>><br>
To: listserv Green Building new<br>
        <<a href="mailto:greenbuilding@lists.bioenergylists.org">greenbuilding@lists.bioenergylists.org</a>>,<br>
        <a href="mailto:healthyhomebuilding@yahoogroups.com">healthyhomebuilding@yahoogroups.com</a><br>
Subject: [Greenbuilding] small in line heat pump<br>
Message-ID:<br>
<br>
<CADj3_s6M8kN0nE_T-N=<a href="mailto:mha3KQhVh-0f%2B1dwdaKG_2myfrC87gg@mail.gmail.com">mha3KQhVh-0f+1dwdaKG_2myfrC87gg@mail.gmail.com</a>><br>
Content-Type: text/plain; charset="iso-8859-1"<br>
<div class="im"><br>
anyone know of a small capacity (12K - 18KBtu) heatpump, suitable for<br>
installation in line with an ERV?<br>
<br>
-a<br>
<br>
<br>
*Alan Abrams**<br>
Abrams Design Build LLC*<br>
</div>*A sustainable approach to beautiful space*<br>
<div class="im"><br>
6411 Orchard Avenue Suite 102<br>
Takoma Park, MD 20912<br>
office  301-270-NET- ZERO <a href="tel:%28301-270-6380" value="+13012706380">(301-270-6380</a>)<br>
fax      <a href="tel:301-270-1466" value="+13012701466">301-270-1466</a><br>
cell     <a href="tel:202-437-8583" value="+12024378583">202-437-8583</a><br>
<a href="mailto:alan@abramsdesignbuild.com">alan@abramsdesignbuild.com</a><br>
</div><a href="http://www.abramsdesignbuild.com" target="_blank">www.abramsdesignbuild.com</a><br>
-------------- next part --------------<br>
An HTML attachment was scrubbed...<br>
URL:<br>
<<a href="http://lists.bioenergylists.org/pipermail/greenbuilding_lists.bioenergyli" target="_blank">http://lists.bioenergylists.org/pipermail/greenbuilding_lists.bioenergyli</a><br>
<a href="http://sts.org/attachments/20120322/57c70aa8/attachment-0001.html" target="_blank">sts.org/attachments/20120322/57c70aa8/attachment-0001.html</a>><br>
<br>
------------------------------<br>
<br>
Message: 2<br>
Date: Thu, 22 Mar 2012 14:25:37 -0400<br>
From: John Straube <<a href="mailto:jfstraube@uwaterloo.ca">jfstraube@uwaterloo.ca</a>><br>
To: Green Building <<a href="mailto:greenbuilding@lists.bioenergylists.org">greenbuilding@lists.bioenergylists.org</a>><br>
<div class="im">Cc: <a href="mailto:healthyhomebuilding@yahoogroups.com">healthyhomebuilding@yahoogroups.com</a><br>
Subject: Re: [Greenbuilding] small in line heat pump<br>
</div>Message-ID: <<a href="mailto:4F6B6EA1.7090401@uwaterloo.ca">4F6B6EA1.7090401@uwaterloo.ca</a>><br>
Content-Type: text/plain; charset="ISO-8859-1"; format=flowed<br>
<div><div class="h5"><br>
Thats a tough one Mr Abrams<br>
To deliver 12 KBtu you need about 400, preferably 450 cfm.  So what kind<br>
of ERV is it? most residential scale ERVs are like 50 to 150 cfm to serve<br>
normal size homes. 400 cfm ERV must be for a commercial use?<br>
If you are talking water source HP, Trane  and Florida Heat Pump (now<br>
bosch) makes a line of water to water heat pumps that small, and you use a<br>
stadard coil in the air stream.<br>
For air to air, all of the standard split units (meaning you can put the<br>
coil in a duct airstream) start at 18 kBtu/hr.  Which requires a lot more<br>
airflow yet again. But Goodman Trane Carrier all make units at 1.5 tons,<br>
they are just not that efficient.<br>
<br>
On 12-03-22 11:43 AM, Alan Abrams wrote:<br>
> anyone know of a small capacity (12K - 18KBtu) heatpump, suitable for<br>
installation in line with an ERV?<br>
><br>
> -a<br>
><br>
><br>
> *Alan Abrams**<br>
> Abrams Design Build LLC*<br>
> /A sustainable approach to beautiful space/<br>
><br>
> 6411 Orchard Avenue Suite 102<br>
> Takoma Park, MD 20912<br>
> office 301-270-NET- ZERO <a href="tel:%28301-270-6380" value="+13012706380">(301-270-6380</a>) fax <a href="tel:301-270-1466" value="+13012701466">301-270-1466</a> cell<br>
> <a href="tel:202-437-8583" value="+12024378583">202-437-8583</a> <a href="mailto:alan@abramsdesignbuild.com">alan@abramsdesignbuild.com</a><br>
> <mailto:<a href="mailto:alan@abramsdesignbuild.com">alan@abramsdesignbuild.com</a>><br>
> <a href="http://www.abramsdesignbuild.com" target="_blank">www.abramsdesignbuild.com</a> <<a href="http://www.abramsdesignbuild.com/" target="_blank">http://www.abramsdesignbuild.com/</a>><br>
><br>
><br>
><br>
> _______________________________________________<br>
> Greenbuilding mailing list<br>
> to Send a Message to the list, use the email address<br>
> <a href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><br>
><br>
> to UNSUBSCRIBE or Change your List Settings use the web page<br>
> <a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b" target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b</a><br>
> <a href="http://ioenergylists.org" target="_blank">ioenergylists.org</a><br>
<br>
--<br>
Prof. John Straube, Ph.D., P.Eng.<br>
Faculty of Engineering<br>
Dept of Civil Engineering / School of Architecture<br>
<br>
<a href="http://www.buildingscience.com" target="_blank">www.buildingscience.com</a><br>
<br>
<br>
<br>
</div></div>------------------------------<br>
<div class="im"><br>
_______________________________________________<br>
Greenbuilding mailing list<br>
to Send a Message to the list, use the email address<br>
<a href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><br>
<br>
to UNSUBSCRIBE or Change your List Settings use the web page<br>
<a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioen
ergylists.org" target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioen<br>
ergylists.org</a><br>
<br>
<br>
</div>End of Greenbuilding Digest, Vol 19, Issue 17<br>
*********************************************<br>
<br>
-----<br>
No virus found in this message.<br>
Checked by AVG - <a href="http://www.avg.com" target="_blank">www.avg.com</a><br>
Version: 2012.0.1913 / Virus Database: 2114/4886 - Release Date: 03/22/12<br>
<div class="HOEnZb"><div class="h5"><br>
_______________________________________________<br>
Greenbuilding mailing list<br>
to Send a Message to the list, use the email address<br>
<a href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><br>
<br>
to UNSUBSCRIBE or Change your List Settings use the web page<br>
<a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a><br>
</div></div></blockquote></div><br></div>