Clarke, even in drain back systems a heat exchanger is usually used. The most practical reason, in your case, would be to maximize stratification. The second valid cause is to limit oxidization, though this can be accounted for by using all non ferrous components. It sounds like you are using unpressurized storage. I have seen two unpressurized drainback systems and one of them used the storage water for the collector "loop" but has all SS components and the draws are always indirect from an unpressurized tank anyway. I see no reason to complicate matters by not using a drain back tank with a HX in the storage tank. I also suspect you can run the pump longer because one needs to keep an eye on the temperature tolerance of the tank.<br>
<br>How many Sq. ft of collectors are you using? It seems like you'll do well with 1000 gallons, your heating load might be less than 20K/hr? I am soon to embark on piping in a 700 gallon off grid with radiant in Bearsville. This system is ground mounted and trenched with no option for a drain back tank so it's going to be a glycol loop. <br>
<br>Jessica <br><br><br><br clear="all"><br>-- <br><br>Jessica Baldwin<br>917-207-2403<br><a href="http://www.solarplumbingdesign.com" target="_blank">Solar Plumbing Design</a><br><br><img src="https://lh3.googleusercontent.com/ifZ2Y8wJzJKRBWl8eTTcVnzVIg-S6jojo2d5rdT0zol46hCCDgMgBiKtO2qupT21mDSlqFsjG-w" height="66" width="200"><br>