    <font face="Helvetica, Arial, sans-serif">Eli is correct re: the BSC
      RR-108 document when he says "</font>The assumption, I guess is
    that air will penetrate the rest of the assembly and show up at the
    bottom of the foam."<br>
    Based on extensive experience, air WILL penetrate drywall and air
    permeable insulations, including dense pack cellulose.<br>
    Exceptional workmanship and simple shapes may be made sufficiently
    airtight, but cannot be practically relied upon. We have seen or
    heard of endless failures of denspack cellulose and fibreglass
    unvented roofs.  Either the interior air must be kept very dry
    during cold weather or condensation must be controlled.<br>
    There are two solutions to controlling condensation by using
    insulation:<br>
    Either <br>
     1. place enough foam outside the air permeable insulation<br>
    or<br>
    2. use sufficent spray foam between the rafters<br>
    to warm the surface above the expected average winter dewpoint of
    the interior air.<br>
    Allow drying to the inside for any moisture that might be in the
    studspace by avoiding very low interior vapor barriers (eg poly, alu
    foil) or finishes.<br>
    <br>
    The old rule of 1/3:2/3 R-value on the interior:exterior of a vapor
    barrier mentioned by Rob Tom has now been superseded by experiments
    and calculations and does not apply to most walls or roofs (but was
    often very conservative)<br>
    <br>
    BSD-163 provides an enhanced explanation of how to calculate the
    appropriate ratio of R-values to avoid condensation and some of the
    basic underlying physics.<br>
    <br>
    <br>
    <br>
    <div class="moz-signature">Dr John Straube, P.Eng. <br>
      <a class="moz-txt-link-abbreviated" href="http://www.BuildingScience.com">www.BuildingScience.com</a></div>
    <br>
    On 12-07-06 12:30 PM, Eli Talking wrote:
    <blockquote cite="mid:33A93518B8FC4269A2BC9212DC1A4011@NewCentury"
      type="cite">
      <br>
      <br>
      At <a class="moz-txt-link-abbreviated" href="http://www.Buildingscience.com">www.Buildingscience.com</a> article   RR-0108_Unvented_Roof_Systems
      describing unvented roofs they reference their concern that the
      foam layer be of sufficient thickness to insure that when air
      reaches the bottom of the foam, the surface temp will be above dew
      point.  The assumption, I guess is that air will penetrate the
      rest of the assembly and show up at the bottom of the foam. 
      However, if the framed rafter was filled with dense pack cellulose
      or fully stuffed fiberglass or roxul, no wires or plumbing are
      installed, and the drywall is managed to be an air barrier, where
      would the air come from?  With no holes in the foam layer, there
      will be no driving pressure to deliver moisture laden air to the
      bottom of foam.  However, more typical rafters with wires,
      recessed electric boxes, unsealed plumbing vents, this would
      provide a path for air to get to the bottom of foam, particularly
      if cold.
      <br>
      <br>
      If this is a problem, this would be a good reason for all the
      insulation to be rigid above the roof sheathing, one of the
      scenarios I described for use with an attic truss.  See below
      <br>
      <br>
      They use a formula of Ratio of thermal resistance above condensing
      surface to
      <br>
      total thermal resistance:
      <br>
      16 ÷ 46 = 0.348
      <br>
      Temperature of Condensing Surface = (ΔT x 0.348) + Outdoor
      Temperature
      <br>
      <br>
      Any thoughts on this recommendation?