    <div class="moz-cite-prefix">Air flow through the window is not the
      same as heat flow and in NO way will it always be in to out, hot
      to cold. Within one window assembly air may even flow in two
      directions, typically in such a case, in at the bottom and out at
      the top. Your simple case is incomplete, but in any case pressures
      do drive air flow, but not temperature difference (although
      pressures can be established because of temperature but that is
      not at all the same thing).<br>
      <br>
      I'd quibble with some other points you raise, but I can't pass on
      the above.<br>
      <br>
    </div>
    <blockquote cite="mid:508DD521.8060007@dnaco.net" type="cite"> Two
      points, in response to two of your posts  (bearing in mind that I
      am speaking on the assumption of a cold climate). <br>
      <br>
      In a cold winter, without extreme exterior humidity and wind - in
      coastal Alaska, for example - the flow through any leaks in the
      window assembly will be from warmer to colder.  The greater the
      temperature differential, the greater the pressure driving the
      leakage.  So, "cold' air should not be leaking into the space
      between panes because the air between panes will be somewhere
      between the interior air temp, at the inside pane, and the air
      temperature against the outside face of the outer pane. 
      Therefore, the air/heat flow will be from inside to out.<br>
      <br>
      Of course, that is the simple model.   Solar loading and wind will
      have their effects.  Of course, the ideal is to have all
      seams/joints in a window unit hermetically sealed, but that's a
      hard thing to achieve and sustain over time. <br>
      <br>
      Adding appropriately sealed layers to the window units will change
      the temperature of the air film under whatever conditions are
      producing condensation, but any window can condense, given the
      "perfect storm" of conditions.  Look to the
      RH/temperature/lifestyle conundrum for each "problem" window.<br>
      <br>
      The solution is to determine the RH/temperature combination that
      allows the problem, then locate the moisture source(s) and change
      them or the actions/assumptions which are causing the elevated RH.<br>
      <br>
      As Mr. Holladay points out, there are several ways to calculate a
      given window's condensation likelihood ranges.  Unfortunately,
      these have to assume a standard set of conditions, which may not
      match those at you home, for any give window or any given time. 
      For all of the complex factors involved, whether or not you will
      have a condensation problem on any given window finally comes down
      to the surface temperature of the window (which as he points out
      varies for different areas of the window) and the dewpoint of the
      film of air actually in contact with that window surface.<br>
      <br>
      Recommendations and RH guideline for house temperatures are useful
      as starting points but, if you have a condensation problem, the
      two approaches are either to experiment  or to have an accurate RH
      gauge to measure the  room air near the window at any given time
      and to get an accurate measurement of the window's surface
      temperature.  You will need some form of  psychrometric chart to
      look up the dewpoint for that temperature and RH.  Someone will
      need to chart those factors over the time the problem occurs, then
      go looking for the excess moisture source(s).<br>
      <br>
      The chart can take a bit of practice to understand but there are
      "slide rule' forms of the psychromatic chart, to more easily find
      dewpoint.  Bachrach makes a sling psychromometer which has a slide
      rule built into the case, but it can be a pain to use.  Electronic
      psychrometers give dewpoint as an automatic function, but are
      significantly more expensive.<br>
      <br>
      Reading the air film temperature or RH is difficult to measure;
      better to use the room air near it and add a cushion.  Trial and
      error should show you a workable adjustment factor.<br>
      <br>
      Reading the window surface temperature can also be tricky.  I have
      the best luck with a quick response contact thermometer.  Remember
      the edge of the glass at the frame is the most likely spot for
      condensation to start.  (IR thermometers do not read accurately on
      glass, unless they can be adjusted for the reflectivity, only
      possible on some expensive models.  You could use a "black body"
      target to get around the reflectivity, but that is probably beyond
      what you need to get into. <br>
      <br>
      I hope this is helpful.<br>
      Bob Klahn<br>
      <div class="moz-cite-prefix">On 10/28/2012 6:30 PM, Sacie
        Lambertson wrote:<br>
      </div>
      <blockquote
cite="mid:CAM6L0t4GLPeOyYVJuDWCCvG9w9CS8LKAob67om8X4_x7ZdUjFQ@mail.gmail.com"
        type="cite"><font><font face="verdana,sans-serif">thanks <font>for

              the suggestion Cor<font>wyn but we have about 50 windows
                in this house, all of them 9 year old Pellas (the only
                manufacturer who would make my custom sized windows <font>within

                  my time frame--a long story here)</font>.  I can't
                possibly imagine building storms for the inside of
                these.<br>
                <br>
                <font>Our indoor humidity is within the <font>suggested
                    range.</font></font><br>
                <br>
                <font>S</font><br>
              </font></font></font></font><br>
        <div class="gmail_quote">On Sun, Oct 28, 2012 at 5:24 PM, Corwyn
          <span dir="ltr"><<a moz-do-not-send="true"
              href="mailto:corwyn@midcoast.com" target="_blank">corwyn@midcoast.com</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div class="im">On 10/28/2012 1:20 PM, Sacie Lambertson
              wrote:<br>
              Our windows are starting to condensate at the base on the<br>
              <blockquote class="gmail_quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex">
                inside.  Many of you have suggested this is the penalty
                of winter.<br>
                Isn't there anything I can do about it?<br>
              </blockquote>
              <br>
            </div>
            See my previous suggestion for interior storm windows.<br>
            <br>
            Here's the basics of when you will get condensation.  When
            the dewpoint temperature of the inside air is a the same as
            (or greater than) the temperature of the inside surface of
            the windows (or anything else in your house), that surface
            will condense water.  So in order to avoid condensation you
            need to either lower the dewpoint of the air inside, by
            reducing the humidity, or increase the temperature of the
            inside surface of the windows.<br>
            <br>
            Whether the humidity is too high is a matter of perspective
            and some controversy.  Get a humidity gauge and measure what
            yours is.  Generally somewhere in the 40% - 60% range is
            recommended, but balance is between being too dry (and the
            dry throat and colds that that produces) and being too wet
            and the mold and mildew (and the allergies that aggravates),
            so decide for yourself.  That said, lowering the humidity
            will reduce the condensation (and vice versa).  One of the
            things we generally see is that as people increase the air
            tightness of their house they need to go from worrying about
            too low humidity to worrying about too high humidity.  At
            that point, you are probably in the place where you will
            need to have supplemental ventilation (for fresh air
            reasons), and an HRV will take care of the humidity issue.<br>
            <br>
            The other way is to raise the temperature of the glass.
             Traditionally this was done by putting the central heating
            output right under the windows so that hot air washed over
            the surface warming it up.  Now, the solution is generally
            to increase the insulation value of the windows. The
            interior storm windows are a cheap way to do this, adding
            about R-2 to a window for about $1.50 per square foot (if
            you make them yourself), I make them for around $4.00 per
            square foot.  Raising the temperature of the glass will also
            increase comfort levels (even at the same air temperature.<br>
            <br>
            Thank You Kindly,<br>
            <br>
            Corwyn<span class="HOEnZb"><font color="#888888"><br>
                <br>
                <br>
                -- <br>
                Topher Belknap<br>
                Green Fret Consulting<br>
                Kermit didn't know the half of it...<br>
                <a moz-do-not-send="true"
                  href="http://www.greenfret.com/" target="_blank">http://www.greenfret.com/</a><br>
                <a moz-do-not-send="true"
                  href="mailto:topher@greenfret.com" target="_blank">topher@greenfret.com</a><br>
                <a moz-do-not-send="true"
                  href="tel:%28207%29%20882-7652" value="+12078827652"
                  target="_blank">(207) 882-7652</a></font></span>
            <div class="HOEnZb">
              <div class="h5"><br>
                <br>
                _______________________________________________<br>
                Greenbuilding mailing list<br>
                to Send a Message to the list, use the email address<br>
                <a moz-do-not-send="true"
                  href="mailto:Greenbuilding@bioenergylists.org"
                  target="_blank">Greenbuilding@bioenergylists.org</a><br>
                <br>
                to UNSUBSCRIBE or Change your List Settings use the web
                page<br>
                <a moz-do-not-send="true"
href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org"
                  target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a><br>
              </div>
            </div>
          </blockquote>
        </div>
        <br>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
    </blockquote>
    <br>
  </body>
</html>