    Thanks Bob, this isn't an argument. We use very different
    definitions of the meaning of several words. In my little world, the
    physics says air flows due to air pressure difference, but heat
    'flows' to a different drummer, and that can be experienced
    empirically. Sounds like life would be easier in your world.  <br>
    <br>
    <blockquote cite="mid:508DEFCF.7090502@dnaco.net" type="cite">
      Peter,<br>
      <br>
      I don't intend to start an argument but have to rise in defense of
      my comments.<br>
      There are three driving forces involved in leakage across the
      window, or any other building surface, 1) air pressure, 2) thermal
      pressure and 3) vapor pressure.  All flows are created by a
      differential in one or more of these.   Both heat and moisture
      ride on air movement.  <br>
      I rarely see simple explanations, or fixes, to this sort of
      problem but physics rules all of them.<br>
      <br>
      Bob Klahn<br>
      <div class="moz-cite-prefix">On 10/28/2012 10:37 PM, Peter Kidd
        wrote:<br>
      </div>
      <blockquote cite="mid:508DEC01.6090108@shaw.ca" type="cite">
        <meta content="text/html; charset=ISO-8859-1"
          http-equiv="Content-Type">
        <div class="moz-cite-prefix">Air flow through the window is not
          the same as heat flow and in NO way will it always be in to
          out, hot to cold. Within one window assembly air may even flow
          in two directions, typically in such a case, in at the bottom
          and out at the top. Your simple case is incomplete, but in any
          case pressures do drive air flow, but not temperature
          difference (although pressures can be established because of
          temperature but that is not at all the same thing).<br>
          <br>
          I'd quibble with some other points you raise, but I can't pass
          on the above.<br>
          <br>
        </div>
        <blockquote cite="mid:508DD521.8060007@dnaco.net" type="cite">
          Two points, in response to two of your posts  (bearing in mind
          that I am speaking on the assumption of a cold climate). <br>
          <br>
          In a cold winter, without extreme exterior humidity and wind -
          in coastal Alaska, for example - the flow through any leaks in
          the window assembly will be from warmer to colder.  The
          greater the temperature differential, the greater the pressure
          driving the leakage.  So, "cold' air should not be leaking
          into the space between panes because the air between panes
          will be somewhere between the interior air temp, at the inside
          pane, and the air temperature against the outside face of the
          outer pane.  Therefore, the air/heat flow will be from inside
          to out.<br>
          <br>
          Of course, that is the simple model.   Solar loading and wind
          will have their effects.  Of course, the ideal is to have all
          seams/joints in a window unit hermetically sealed, but that's
          a hard thing to achieve and sustain over time. <br>
          <br>
          Adding appropriately sealed layers to the window units will
          change the temperature of the air film under whatever
          conditions are producing condensation, but any window can
          condense, given the "perfect storm" of conditions.  Look to
          the RH/temperature/lifestyle conundrum for each "problem"
          window.<br>
          <br>
          The solution is to determine the RH/temperature combination
          that allows the problem, then locate the moisture source(s)
          and change them or the actions/assumptions which are causing
          the elevated RH.<br>
          <br>
          As Mr. Holladay points out, there are several ways to
          calculate a given window's condensation likelihood ranges. 
          Unfortunately, these have to assume a standard set of
          conditions, which may not match those at you home, for any
          give window or any given time.  For all of the complex factors
          involved, whether or not you will have a condensation problem
          on any given window finally comes down to the surface
          temperature of the window (which as he points out varies for
          different areas of the window) and the dewpoint of the film of
          air actually in contact with that window surface.<br>
          <br>
          Recommendations and RH guideline for house temperatures are
          useful as starting points but, if you have a condensation
          problem, the two approaches are either to experiment  or to
          have an accurate RH gauge to measure the  room air near the
          window at any given time and to get an accurate measurement of
          the window's surface temperature.  You will need some form of 
          psychrometric chart to look up the dewpoint for that
          temperature and RH.  Someone will need to chart those factors
          over the time the problem occurs, then go looking for the
          excess moisture source(s).<br>
          <br>
          The chart can take a bit of practice to understand but there
          are "slide rule' forms of the psychromatic chart, to more
          easily find dewpoint.  Bachrach makes a sling psychromometer
          which has a slide rule built into the case, but it can be a
          pain to use.  Electronic psychrometers give dewpoint as an
          automatic function, but are significantly more expensive.<br>
          <br>
          Reading the air film temperature or RH is difficult to
          measure; better to use the room air near it and add a
          cushion.  Trial and error should show you a workable
          adjustment factor.<br>
          <br>
          Reading the window surface temperature can also be tricky.  I
          have the best luck with a quick response contact thermometer. 
          Remember the edge of the glass at the frame is the most likely
          spot for condensation to start.  (IR thermometers do not read
          accurately on glass, unless they can be adjusted for the
          reflectivity, only possible on some expensive models.  You
          could use a "black body" target to get around the
          reflectivity, but that is probably beyond what you need to get
          into. <br>
          <br>
          I hope this is helpful.<br>
          Bob Klahn<br>
          <div class="moz-cite-prefix">On 10/28/2012 6:30 PM, Sacie
            Lambertson wrote:<br>
          </div>
          <blockquote
cite="mid:CAM6L0t4GLPeOyYVJuDWCCvG9w9CS8LKAob67om8X4_x7ZdUjFQ@mail.gmail.com"
            type="cite"><font><font face="verdana,sans-serif">thanks <font>for



                  the suggestion Cor<font>wyn but we have about 50
                    windows in this house, all of them 9 year old Pellas
                    (the only manufacturer who would make my custom
                    sized windows <font>within my time frame--a long
                      story here)</font>.  I can't possibly imagine
                    building storms for the inside of these.<br>
                    <br>
                    <font>Our indoor humidity is within the <font>suggested


                        range.</font></font><br>
                    <br>
                    <font>S</font><br>
                  </font></font></font></font><br>
            <div class="gmail_quote">On Sun, Oct 28, 2012 at 5:24 PM,
              Corwyn <span dir="ltr"><<a moz-do-not-send="true"
                  href="mailto:corwyn@midcoast.com" target="_blank">corwyn@midcoast.com</a>></span>
              wrote:<br>
              <blockquote class="gmail_quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex">
                <div class="im">On 10/28/2012 1:20 PM, Sacie Lambertson
                  wrote:<br>
                  Our windows are starting to condensate at the base on
                  the<br>
                  <blockquote class="gmail_quote" style="margin:0 0 0
                    .8ex;border-left:1px #ccc solid;padding-left:1ex">
                    inside.  Many of you have suggested this is the
                    penalty of winter.<br>
                    Isn't there anything I can do about it?<br>
                  </blockquote>
                  <br>
                </div>
                See my previous suggestion for interior storm windows.<br>
                <br>
                Here's the basics of when you will get condensation.
                 When the dewpoint temperature of the inside air is a
                the same as (or greater than) the temperature of the
                inside surface of the windows (or anything else in your
                house), that surface will condense water.  So in order
                to avoid condensation you need to either lower the
                dewpoint of the air inside, by reducing the humidity, or
                increase the temperature of the inside surface of the
                windows.<br>
                <br>
                Whether the humidity is too high is a matter of
                perspective and some controversy.  Get a humidity gauge
                and measure what yours is.  Generally somewhere in the
                40% - 60% range is recommended, but balance is between
                being too dry (and the dry throat and colds that that
                produces) and being too wet and the mold and mildew (and
                the allergies that aggravates), so decide for yourself.
                 That said, lowering the humidity will reduce the
                condensation (and vice versa).  One of the things we
                generally see is that as people increase the air
                tightness of their house they need to go from worrying
                about too low humidity to worrying about too high
                humidity.  At that point, you are probably in the place
                where you will need to have supplemental ventilation
                (for fresh air reasons), and an HRV will take care of
                the humidity issue.<br>
                <br>
                The other way is to raise the temperature of the glass.
                 Traditionally this was done by putting the central
                heating output right under the windows so that hot air
                washed over the surface warming it up.  Now, the
                solution is generally to increase the insulation value
                of the windows. The interior storm windows are a cheap
                way to do this, adding about R-2 to a window for about
                $1.50 per square foot (if you make them yourself), I
                make them for around $4.00 per square foot.  Raising the
                temperature of the glass will also increase comfort
                levels (even at the same air temperature.<br>
                <br>
                Thank You Kindly,<br>
                <br>
                Corwyn<span class="HOEnZb"><font color="#888888"><br>
                    <br>
                    <br>
                    -- <br>
                    Topher Belknap<br>
                    Green Fret Consulting<br>
                    Kermit didn't know the half of it...<br>
                    <a moz-do-not-send="true"
                      href="http://www.greenfret.com/" target="_blank">http://www.greenfret.com/</a><br>
                    <a moz-do-not-send="true"
                      href="mailto:topher@greenfret.com" target="_blank">topher@greenfret.com</a><br>
                    <a moz-do-not-send="true"
                      href="tel:%28207%29%20882-7652"
                      value="+12078827652" target="_blank">(207)
                      882-7652</a></font></span>
                <div class="HOEnZb">
                  <div class="h5"><br>
                    <br>
                    _______________________________________________<br>
                    Greenbuilding mailing list<br>
                    to Send a Message to the list, use the email address<br>
                    <a moz-do-not-send="true"
                      href="mailto:Greenbuilding@bioenergylists.org"
                      target="_blank">Greenbuilding@bioenergylists.org</a><br>
                    <br>
                    to UNSUBSCRIBE or Change your List Settings use the
                    web page<br>
                    <a moz-do-not-send="true"
href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org"
                      target="_blank">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a><br>
                  </div>
                </div>
              </blockquote>
            </div>
            <br>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <br>
            <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
          </blockquote>
          <br>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <br>
          <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
        </blockquote>
        <br>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a moz-do-not-send="true" class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a moz-do-not-send="true" class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a class="moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a class="moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</a></pre>
    </blockquote>
    <br>
  </body>
</html>