    <div class="moz-cite-prefix"><font face="Helvetica, Arial,
        sans-serif">What do I think is incorrect and misleading? For a
        start<br>
        1. long screws are structural. <br>
        2. you cannot screw a long screw into an assembly without
        torqueing off the head<br>
        3. you cant find #10 screws in long lengths<br>
        4. fastening is the over riding cost for attaching foam through
        furring to wood frame walls<br>
        <br>
        How does this impede progress?<br>
        A major improvement in durability and energy performance can be
        achieved by applying exterior insulation to wood and steel
        framed buildings.  <br>
        Unfounded or out-of-context statements like 1 thru 4 cause
        people to not attempt this technique. They dont even try.  Once
        someone builds a few houses, often just part of a single one, it
        becomes clear that 1 to 4 are not true.  I have seen this happen
        repeatedly over the last decade. People in workshops, seminars,
        conferences, and design offices regularily say these things
        (another common one is "a few screws cant hold up "heavy" siding
        like fibre cement).  I have been showing case studies and doing
        demonstrations for more than 10 years to answer these types of
        questions.  When people actually get around to trying this,
        wether architect, code official, contractor, trade, or home
        handyman, those objections go away. Because they are not true.
        This is the reason I care so much about the topic and why it frustrates
        me.<br>
        <br>
        This thread was not about EIFS.  It was about Bill Allens
        question on fastening foam and furring to walls.  I mention EIFS
        and roofing since they make and use the fasteners required for
        attach foam. You dont need washers when attaching wood furring
        through foam.  So dont buy the washer.  Hence the prices I
        quoted are valid. You can try and use adhesives for attaching
        siding to a wall, but I dont think it will work, and wont
        comment further till I try it.<br>
        <br>
        Fewer large and more expensive screws at wider spacings can work
        to hold up the cladding, but the suction wind loads tend to
        cause the furring strip (1x3 and 1x4) to fail in bending between
        widely spaced screws.  You dont need a big screw for spacings 
        of 2 to 3 square feet of area.  Once you go beyond that, you get
        to vertical spacings of 24 to 36" (and yes 1/4" and 5/16" dia
        screws are needed at that spacing) but then the suction loads of
        the cladding cause 1x furring to fail in bending.  So you would
        have to use 2x furring.  Technically fine (36"x24" spacings of
        5/16" screws will work) but the cost and resource use of 2x3 or
        2x4 furring tends to argue against it. <br>
        <br>
        Again, I want to emphasize, furring strips through 2, 3, 4" and
        more of foam has been done in dozens of states and many
        provinces on hundreds of projects (that I know about, likely
        much much more) and this is no more, often less, challenging
        than figuring out how to attach drywall to framing.  The ONLY
        thing that is difficult to do is find the screws at a retail
        level.  It regularly is challenging for people who come across
        the idea for the first time to understand and believe the idea.<br>
        <br>
        <br>
      </font>
      <div class="moz-signature">Dr John Straube, P.Eng. <br>
        <a class="moz-txt-link-abbreviated" href="http://www.BuildingScience.com">www.BuildingScience.com</a><br>
        <br>
      </div>
      On 12-11-15 1:04 PM, John Salmen wrote:<br>
    </div>
    <blockquote cite="mid:007101cdc35b$b5cec680$216c5380$@ca"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=ISO-8859-1">
      <meta name="Generator" content="Microsoft Word 12 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:Helvetica;
        panose-1:2 11 6 4 2 2 2 2 2 4;}
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Tahoma;
        panose-1:2 11 6 4 3 5 4 4 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman","serif";
        color:black;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";
        color:black;}
p.MsoAcetate, li.MsoAcetate, div.MsoAcetate
        {mso-style-priority:99;
        mso-style-link:"Balloon Text Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:8.0pt;
        font-family:"Tahoma","sans-serif";
        color:black;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:Consolas;
        color:black;}
span.EmailStyle19
        {mso-style-type:personal-reply;
        font-family:"Calibri","sans-serif";
        color:#1F497D;}
span.BalloonTextChar
        {mso-style-name:"Balloon Text Char";
        mso-style-priority:99;
        mso-style-link:"Balloon Text";
        font-family:"Tahoma","sans-serif";
        color:black;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:72.0pt 72.0pt 72.0pt 72.0pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">What
            is incorrect and false and impedes what kind of progress?<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">I
            am not talking about mechanically fastening foam we are
            talking about fastening wood against foam through to
            framing. EIFS screws and washers like dekfast and windlock
            are great for attaching foam (if you need to) but you need
            the washer so still about .35 per screw <u>and </u>washer
            – and it is usually minimum1 screw per square foot for eifs.
            That is the equivalent cost of 2” of eps (I pay about .18
            per board foot for eps). I am not sure what is progressive
            about thousands of screws and plastic washers - I prefer
            foam adhesives<o:p></o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D">So
            for mechanically fastening battens or wood components
            against foam ONE large head structural screw at framing
            intervals at a cost of .30 per screw is I think a pretty
            responsible approach  (don’t buy them at home despot). And
            yes screw heads snapping or screws bending is a common
            problem when embedding a long low strength metal screw
            1-1/2” into spf framing. And I am not sure why there would
            excuses if there wasn’t a perceived problem.<o:p></o:p></span></p>
        <span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p></o:p></span>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
style="font-size:11.0pt;font-family:"Calibri","sans-serif";color:#1F497D"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #B5C4DF
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                  lang="EN-US">From:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext"
                lang="EN-US"> John Straube [<a class="moz-txt-link-freetext" href="mailto:jfstraube@gmail.com">mailto:jfstraube@gmail.com</a>]
                <br>
                <b>Sent:</b> November-15-12 6:36 AM<br>
                <b>To:</b> John Salmen<br>
                <b>Cc:</b> <a class="moz-txt-link-abbreviated" href="mailto:george@houseisasystem.com">george@houseisasystem.com</a>; 'Green Building'<br>
                <b>Subject:</b> Re: [Greenbuilding] Insulation fasteners<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <p class="MsoNormal" style="margin-bottom:12.0pt"><span
              style="font-family:"Helvetica","sans-serif"">John,
              much of what you say is not correct. This bothers me
              because I routinely hear these false claims made, and this
              incorrect information impedes progress in making good
              energy efficient buildings (something I know you care
              about).<br>
              <b>You can get long screws that are not "structural
                screws".</b>  I know, because we and many others
              installing thick layers of foam insulation and have been
              doing this for years. There must be a few dozen case
              studies alone on our website.<br>
              Yes, long structural screws are what you find at Home
              Depot, but these expensive and problematic in a number of
              ways.<br>
              It is quite possible to get #10 or #12 screws in lengths
              of 6" and up.  #10 is typically only available to about 6"
              length, and then #12 to about 12 or 14" long, and then you
              are up to #14 / 1/4" dia for lengths up to 20" or so. We
              regularily find that a #12x6" can be cheaper than a #10x6"
              and thus use them, but #10 is what we have always tested
              in the lab because they are the smallest available and
              hence the most flexible with the lowest pullout loads. 
              Their heads DO NOT torque off when used to attach foam.  
              They are NOT intended for screwing through solid wood but
              through insulation, which is why they work perfectly
              well.  Millions of 6" long or longer screws are installed
              every year through foam in the commercial low-slope
              roofing and EIFS industry (see for example Wind-lok for
              #10x6" long).  This is the first stop if you are looking
              for long thin screws that have corrosion resistance, are
              easy to install and affordable.   These products in these
              building niches all have a long track record of being
              installed  by the thousands without problems of torquing
              off heads, driver slippage, bending, or whatever other
              excuses I have heard. They have been designed for
              embedding about 1 to 1.5" in wood after screwing through
              4-12" of roof  or EIFS insulation. What is not easy for
              individuals and small contractors is finding these screws
              because they are typically carried by larger supply houses
              and commercial sales outlets.  If more people start super
              insulating their houses, I am pretty sure the fastener
              industry will respond by marketing their roof screws as
              wall screws and the problem will go away.<br>
              <br>
              The HeadLok screws are great for many structural
              applications, but I think these are used for attaching
              foam and furring only because they are available at retail
              outlets. There are quite nice, but are usually twice as
              expensive as the alternatives (40 cents each and up), and
              often three times the cost retail (eg we get supply house
              prices of 12 cents on a #10x6" and the contractor tells us
              that HeadLok or GRK cost $150 for a 250 pack).  <br>
              <br>
              <b>The screws are also NOT the most expensive part of the
                assembly.</b>  Not even close.<br>
              If you purchase relatively heavy 6" long screws from, say,
              here <br>
              <a moz-do-not-send="true"
                href="http://www.bestmaterials.com/detail.aspx?ID=9221">http://www.bestmaterials.com/detail.aspx?ID=9221</a><br>
              They cost maybe 20 cents each (these are #12-14 screws)  
              Not the cheapest source but not bad.  Often available for
              15 cents.  If you use one screw every 12" vertically and
              24" horizontally (pretty conservative), that is 1 screw
              per 2 square feet or about 10 cents/square foot at 20
              cents each.  When labour is added, the screw might be 3
              times as expensive (30 cents /square foot).<br>
              4" of polyiso will cost something in the order of $2 to
              $2.50 per square foot, making the screw less than 5% of
              the cost of materials for the exterior insulation (adding
              the cost of furring strips changes little). 4" of EPS will
              be about $1.50.  With labour, the screw is still around
              10% or less.<br>
              <br>
            </span><o:p></o:p></p>
          <div>
            <p class="MsoNormal">Dr John Straube, P.Eng. <br>
              <a moz-do-not-send="true"
                href="http://www.BuildingScience.com">www.BuildingScience.com</a><o:p></o:p></p>
          </div>
          <p class="MsoNormal">On 12-11-14 11:10 PM, John Salmen wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <pre>When you get into long screws they are structural screws - equivalent to a<o:p></o:p></pre>
          <pre>3/8" bolt (actually better). For sure they are overkill but that is where<o:p></o:p></pre>
          <pre>eng. crosses practicality. When you increase length on anything the design<o:p></o:p></pre>
          <pre>requirements for actually getting the screw into the material override the<o:p></o:p></pre>
          <pre>design criteria for loading. The reason being that you cannot screw a long<o:p></o:p></pre>
          <pre>softmetal screw into an assembly without torqueing off the head. - I don't<o:p></o:p></pre>
          <pre>even think you can even find a #10 standard soft metal screw in long lengths<o:p></o:p></pre>
          <pre>anymore - I remember putting an order in from one manuf. a decade ago and<o:p></o:p></pre>
          <pre>half the screws were thrown away from having heads torqued off. 1/4" and<o:p></o:p></pre>
          <pre>3/8" lag bolts would also self destruct far too often in application to make<o:p></o:p></pre>
          <pre>them practical for a load that an 1/8" of metal would carry. We are talking<o:p></o:p></pre>
          <pre>about crews that have to install a lot of bolts/screws in a day and wasting<o:p></o:p></pre>
          <pre>their time with defective material is an overriding consideration.<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>Headlok screws that I mentioned will cost about .30 per for 6" and about .50<o:p></o:p></pre>
          <pre>per for 8" and each screw will do what is supposed to do. They drive in<o:p></o:p></pre>
          <pre>quickly and perfectly each time. They have a large wafer head equivalent to<o:p></o:p></pre>
          <pre>a washer so one screw generally takes the place of at least 2 screws in<o:p></o:p></pre>
          <pre>design. <o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>Fastening is the overriding cost in assemblies at this point and it is split<o:p></o:p></pre>
          <pre>between the cost of the fastener and the time taken to fasten. That is why<o:p></o:p></pre>
          <pre>most buildings are being put together with adhesives.<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>  <o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>-----Original Message-----<o:p></o:p></pre>
          <pre>From: Greenbuilding [<a moz-do-not-send="true" href="mailto:greenbuilding-bounces@lists.bioenergylists.org">mailto:greenbuilding-bounces@lists.bioenergylists.org</a>]<o:p></o:p></pre>
          <pre>On Behalf Of George J. Nesbitt<o:p></o:p></pre>
          <pre>Sent: November-14-12 6:57 PM<o:p></o:p></pre>
          <pre>To: <a moz-do-not-send="true" href="mailto:jfstraube@gmail.com">jfstraube@gmail.com</a>; Green Building<o:p></o:p></pre>
          <pre>Subject: Re: [Greenbuilding] Insulation fasteners<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>I'm about to screw through 4-1/2" of polyiso, I can only find 6" screws<o:p></o:p></pre>
          <pre>affordably ($13/100ea), longer screws are $1ea. Sources & prices for 6"+<o:p></o:p></pre>
          <pre>#10 screws?<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>On 11/14/2012 7:53 AM, John Straube wrote:<o:p></o:p></pre>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <pre>We have tested up to 8" of foam (EPS, XPS is stronger) with #10 screws and<o:p></o:p></pre>
          </blockquote>
          <pre>furring strips. Works fine with siding ( safety factor of more than 10).<o:p></o:p></pre>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <pre>3/8" lags is crazy: never need it. The foam provides a lot of the<o:p></o:p></pre>
          </blockquote>
          <pre>strength.<o:p></o:p></pre>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <pre>Check our buildingscience.com website or my book for more detail on how<o:p></o:p></pre>
          </blockquote>
          <pre>this works.<o:p></o:p></pre>
          <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
            <pre><o:p> </o:p></pre>
            <pre>Sent wirelessly from my BlackBerry device on the Bell network.<o:p></o:p></pre>
            <pre><o:p> </o:p></pre>
            <pre>-----Original Message-----<o:p></o:p></pre>
            <pre>From: Clarke Olsen <a moz-do-not-send="true" href="mailto:colsen@fairpoint.net"><colsen@fairpoint.net></a><o:p></o:p></pre>
            <pre>Sender: "Greenbuilding" <o:p></o:p></pre>
            <pre><a moz-do-not-send="true" href="mailto:greenbuilding-bounces@lists.bioenergylists.org"><greenbuilding-bounces@lists.bioenergylists.org></a><o:p></o:p></pre>
            <pre>Date: Wed, 14 Nov 2012 09:50:23<o:p></o:p></pre>
            <pre>To: Green Building<a moz-do-not-send="true" href="mailto:greenbuilding@lists.bioenergylists.org"><greenbuilding@lists.bioenergylists.org></a><o:p></o:p></pre>
            <pre>Reply-To: Green Building <a moz-do-not-send="true" href="mailto:greenbuilding@lists.bioenergylists.org"><greenbuilding@lists.bioenergylists.org></a><o:p></o:p></pre>
            <pre>Subject: Re: [Greenbuilding] Insulation fasteners<o:p></o:p></pre>
            <pre><o:p> </o:p></pre>
            <pre>_______________________________________________<o:p></o:p></pre>
            <pre>Greenbuilding mailing list<o:p></o:p></pre>
            <pre>to Send a Message to the list, use the email address <o:p></o:p></pre>
            <pre><a moz-do-not-send="true" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><o:p></o:p></pre>
            <pre><o:p> </o:p></pre>
            <pre>to UNSUBSCRIBE or Change your List Settings use the web page <o:p></o:p></pre>
            <pre><a moz-do-not-send="true" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b</a><o:p></o:p></pre>
            <pre>ioenergylists.org _______________________________________________<o:p></o:p></pre>
            <pre>Greenbuilding mailing list<o:p></o:p></pre>
            <pre>to Send a Message to the list, use the email address <o:p></o:p></pre>
            <pre><a moz-do-not-send="true" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><o:p></o:p></pre>
            <pre><o:p> </o:p></pre>
            <pre>to UNSUBSCRIBE or Change your List Settings use the web page <o:p></o:p></pre>
            <pre><a moz-do-not-send="true" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.b</a><o:p></o:p></pre>
            <pre>ioenergylists.org<o:p></o:p></pre>
            <pre><o:p> </o:p></pre>
          </blockquote>
          <pre><o:p> </o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>--<o:p></o:p></pre>
          <pre>George J. Nesbitt, Environmental Design / Build, Building Performance<o:p></o:p></pre>
          <pre>Contractor HERS I Verifier & HERS II Rater, GreenPoint Rater new & existing<o:p></o:p></pre>
          <pre>SF & MF, CABEC CEPE (Certified Energy Plans Examiner), Certified Passive<o:p></o:p></pre>
          <pre>House Consultant, BPI Multifamily Analyst, <a moz-do-not-send="true" href="http://www.houseisasystem.com">www.houseisasystem.com</a>, (510)<o:p></o:p></pre>
          <pre>655-8532 office, (510) 599-5708 mobile<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>_______________________________________________<o:p></o:p></pre>
          <pre>Greenbuilding mailing list<o:p></o:p></pre>
          <pre>to Send a Message to the list, use the email address<o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.org</a><o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre>to UNSUBSCRIBE or Change your List Settings use the web page<o:p></o:p></pre>
          <pre><a moz-do-not-send="true" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioener">http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioener</a><o:p></o:p></pre>
          <pre>gylists.org<o:p></o:p></pre>
          <pre><o:p> </o:p></pre>
          <pre><o:p> </o:p></pre>
        </blockquote>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
    </blockquote>
    <br>
  </body>
</html>