<DIV><FONT size=4>Thanks for all the thoughtful replies to my original 
post.  The result of input and further thought is that I am returning to 
plan “A” to mount all 12” EPS foam insulation on top of the structural roof 
sheathing.  This is simpler than what I proposed below.  Installing a 
long strip of foam during the construction between top chord rafters has a lot 
of potential problems.  I plan to install 2x4 furring strips at 2’oc that I 
will predrill for accuracy of alignment of screw.  I will also countersink 
with 1” deep x .5”round hole that will allow the head of the screw to be .5” 
above the deck, giving the screw 1 additional inch of penetration, allowing a 
shorter screw.  Also, the counter sink hole can be filled with can foam to 
block the thermal weakness from the conductive screws.  By using full 2x’s 
for furring strips on both roof and walls, the finish siding and corrugated 
metal roofing can be fastened with old fashioned nails, reducing the time and 
cost of installing screws for finished materials which would be needed if the 
alternative 3”strips of 3/4” plywood is used.  </FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>I understand the method of installing a foam block in faming 
cavity slightly smaller so that a seal can be placed on one side of foam, 
pressed against one side of cavity, leaving a gap to be filled with can foam. I 
used this method during my deep energy retrofit in my home. In my case, I 
installed 3” foam below a cathedral ceiling and 3” foam over old plywood 
siding.  To create continuity, I installed foam blocks in stud cavity as 
described above that connected these 2 elements of the thermal envelope.  
It is certainly tedious and vulnerable to execution flaws. My preferred method 
for making that connection is to leave the cavity to be filled with a 
professional sight applied insulation.  However, the situation I described, 
I was managing a 6” foam above the roof deck to be air tight, therefore, sealing 
was not so critical.  In the original concept, it would be replacing the 
air permeable fiberglass.  </FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>Additional questions I will be posting in a separate message 
is sealing the plywood seams and using framing cavities for ERV duct 
chases.  </FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>Eli </FONT></DIV>
<DIV><FONT size=4><A 
href="http://www.conservationarchitect.net">www.conservationarchitect.net</A> 
</FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>Another sit</FONT></DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">
<DIV style="FONT: 10pt tahoma">
<DIV> </DIV>
<DIV style="BACKGROUND: #f5f5f5">
<DIV style="font-color: black"><B>From:</B> <A title=elitalking@rockbridge.net 
href="mailto:elitalking@rockbridge.net">Eli Talking</A> </DIV>
<DIV><B>Sent:</B> Thursday, January 03, 2013 11:04 AM</DIV>
<DIV><B>To:</B> <A title=jfstraube@uwaterloo.ca 
href="mailto:jfstraube@uwaterloo.ca">jfstraube@uwaterloo.ca</A> ; <A 
title=archilogic@chaffyahoo.ca 
href="mailto:archilogic@chaffyahoo.ca">archilogic@chaffyahoo.ca</A> ; <A 
title=greenbuilding@lists.bioenergylists.org 
href="mailto:greenbuilding@lists.bioenergylists.org">Green Building</A> </DIV>
<DIV><B>Subject:</B> [Greenbuilding] Foam installed between framing during 
framing</DIV></DIV></DIV>
<DIV> </DIV></DIV>
<DIV 
style="FONT-STYLE: normal; DISPLAY: inline; FONT-FAMILY: 'Calibri'; COLOR: #000000; FONT-SIZE: small; FONT-WEIGHT: normal; TEXT-DECORATION: none">
<DIV dir=ltr>
<DIV style="FONT-FAMILY: 'Times New Roman'; COLOR: #000000; FONT-SIZE: 14pt">
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>I am wondering if it would be reasonable to install accurately 
precut eps foam between joist, rafters, or top chord of truss during the framing 
to achieve a cheap relatively tight installation when compared to fiberglass 
with the air seal being achieve outside the framing with continuous 6” eps foam 
managed for air tightness.  More detailed description is below.  
</FONT></DIV>
<DIV> </DIV>
<DIV><EM>From: John Straube </EM></DIV>
<DIV><EM>Sent: Wednesday, November 28, 2012 1:13 PM </EM></DIV>
<DIV><EM></EM> </DIV>
<DIV><EM>Experience has taught those who have built a few of these 
externally-insulated buildings that they can be easier to build too.  This 
means one has to learn how to handle the remaining challenges</EM></DIV>
<DIV><EM>1. how to find low cost long screws that screw in quickly and 
easily</EM></DIV>
<DIV><EM>2. the furring needed to allow for easy cladding fastening</EM></DIV>
<DIV><EM>3. the details at window and door openings required to mee</EM></DIV>
<DIV><EM>Point 3 is still evolving and improving.</EM></DIV>
<DIV> </DIV>
<DIV>My comments:</DIV>
<DIV>I am designing a house mounting eps on exterior of framing.  I found a 
source of eps that is a lower price than fiberglass/R.  By making it on the 
outside, I avoid the conflict with wires and plumbing commonly installed in the 
framing and achieve continuity.   Also, the framing is inside the 
thermal envelope and therefore near the conditioned temp.  I am addressing 
the three issues John brought up.  </DIV>
<DIV> </DIV>
<DIV>I found a source of long screws. </DIV>
<DIV><A 
href="http://www.loghomestore.com/1748-headloc-panel-fasteners-9-to-18-inch.php">http://www.loghomestore.com/1748-headloc-panel-fasteners-9-to-18-inch.php</A></DIV>
<DIV><FONT size=4>Prices seem reasonable.  Far less than GKR screws that I 
love.  However, the screws are a significant cost.  My original intent 
was to mount 12”eps over the roof sheathing.  However, using a spacing of 
2’oc on furring strips that are also at 2’oc, it results in 4 screws/4sf, or 1 
screw/sf.  On the walls, my 6”foam is setting on the foundation with no 
significant loading except for wind suction.  My site is windy.  For 
this I need am planning a 9.5” screw at </FONT></DIV>
<DIV><FONT size=4>$.50/screw in bulk.  However, the thicker roof would need 
16” screw for $1.22/screw.  That is a significant sf upcharge.  The 
12”eps is only $1.56/sf.  I am aspiring to keeping the cost down to create 
more access for high performance.  As a result of this cost, I made the 
recommendation that we insulate the ceiling of continuous 4” eps  mounted 
below cheap plane jane truss to achieve the continuous thick air barrier with 
cellulose toped off to achieve higher R value.  I believe this is the most 
cost affective way to top off the thermal envelope.  However, my clients 
want to develop the attic. Therefore, we are back to wrapping the insulation 
above the roof sheathing.  However, because of the cost of the fasteners, I 
am looking to skin it with only 6” foam to achieve thick air barrier and put 
some insulation in between attic truss top chord to increase the R value.  
Fiberglass would be the easiest.  Because of the above roof eps, it 
probably would be ok, even though it is air pervious.  I would follow <A 
href="http://www.buildingscience.com">www.buildingscience.com</A> ‘s 
recommendation for proportion of air pervious to non air pervious to insure 
inner most foam temp remains above dew point in winter with 50% relative 
humidity in house.   </FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>However, I am wondering if you could precisely cut eps foam to 
the exact 22.5” spacing between truss top chord mounted at 24”oc.  I see 
this as being installed during the framing with a friction fit.  Since the 
top 6” insulation achieves the air barrier requirement, I would not think 
additional sealing would be needed.  Even without sealing, the nature of 
eps would be much tighter than fiberglass.  It also turns out it is less 
expensive.  This could also be done at the band joist.  Installing 
during the framing allows the foam to be used as a spacer to create a tight fit 
that would be difficult to achieve after framing.  However, I have not seen 
it done this way.  Therefore, what are the risk that I am not seeing?  
Or is this a reasonable idea to increase R value at a low cost?</FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>List input is always appreciated.  </FONT></DIV>
<DIV><FONT size=4></FONT> </DIV>
<DIV><FONT size=4>Eli</FONT></DIV>
<DIV><FONT size=4><A 
href="http://www.conservationarchitect.net">www.conservationarchitect.net</A> 
</FONT></DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV> </DIV></DIV></DIV>
<P>
<HR>
_______________________________________________<BR>Greenbuilding mailing 
list<BR>to Send a Message to the list, use the email 
address<BR>Greenbuilding@bioenergylists.org<BR><BR>to UNSUBSCRIBE or Change your 
List Settings use the web 
page<BR>http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</DIV></DIV></DIV></BODY></HTML>