<DIV>Thanks John for replying to my message.  I work in a mixed climate of 
Western Virginia.  </DIV>
<DIV> </DIV>
<DIV>Coming from you, I take your comments about the fluctuation of humidity in 
framing outside the thermal envelope very seriously.  My thought was that I 
am creating a similar condition to drafty old houses that never rot because they 
have lots of air flowing through them.  Therefore whatever weather driven 
moisture gets through the siding will dry out.  My intention was to put 
flashing at the bottom of the wall to drain any bulk liquid.  However, I 
have not considered the impact of fluctuating humidity on the dimension of the 
framing that my proposed panels were to cover to the interior.  So I may 
reconsider.  John, in you considerable experience have you seen the 
interior approach tried similar to what I describe?</DIV>
<DIV> </DIV>
<DIV>I have renovated my home that had conventional fiberglass batts and plywood 
sheathing by installing 3” iso foam and mounting  3”x3/4” sheathing strips 
to mount plywood siding to.  This is similar to what you 
recommend.   In the future with this approach I would likely use 2x3’s 
for furring.  If the attic is kept inside the thermal envelope, I will 
continue the insulation over the roof sheathing avoiding thermal bridge at 
eave.  If using eps foam, I would ventilate with purlins under metal roof 
and design positive draft ventilation to carry away any interior driven vapor 
that would migrate through the eps foam.  </DIV>
<DIV> </DIV>
<DIV>This house in South Carolina had trouble with rotting osb above a rafter 
cavity filled with vapor permeable open cell foam.  <A 
title=http://www.greenbuildingadvisor.com/blogs/dept/musings/open-cell-spray-foam-and-damp-roof-sheathing 
href="http://www.greenbuildingadvisor.com/blogs/dept/musings/open-cell-spray-foam-and-damp-roof-sheathing">http://www.greenbuildingadvisor.com/blogs/dept/musings/open-cell-spray-foam-and-damp-roof-sheathing</A></DIV>
<DIV>This article does not give firm conclusions.  The solution this author 
proposes of creating a vapor armor using closed cell foam, is one 
approach.  However, I believe the problem was that building paper acted as 
a vapor barrier, raising the dew point and hence condensation and rotting.  
I would propose that this problem would not have occurred if the vapor had space 
to draft out once it had migrated through the foam.  If installed properly, 
the interior draft would only be vapor, not air.  The air draft would come 
completely from exterior air.  Therefore the ventilation above the foam 
does not increase air draft in the building.  I am curious to  know if 
vapor that condenses inside a vapor permeable foam can evaporate again and 
continue drafting through once the temperature has risen.  </DIV>
<DIV> </DIV>
<DIV>John’s Comment:</DIV>
<DIV>The approach does solve the rather major thermal bridges of the floor 
penetrations throough the wall.  It does breaks the thermal bridge of the 
plates and studs though.  </DIV>
<DIV> </DIV>
<DIV>My Comment:</DIV>
<DIV>A multiple story building would still have thermal bridging of joist 
penetrating the thermal envelope.  I would have professional insulators 
install open cell foam.  However at the bottom floor and at the top flat 
ceiling allows perfect continuity(no thermal bridges).   The problems 
I have become aware of with tight houses that have siding nailed directly to 
sheathing that that has solid foam on the other side, is that weather driven 
moisture gets trapped in them and the common practice draft through the house is 
not available to dry it out, causing rot.  </DIV>
<DIV> </DIV>
<DIV>My incentive for the method I was describing was to eliminate one layer of 
framing by making the structure and the drain dry plain the same.  Also, I 
was looking for the panels to allow a possible retrofit application.  
However, your comments give me cause for concern.  </DIV>
<DIV> </DIV>
<DIV>Eli </DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>-----Original Message----- </DIV>
<DIV>From: John Straube </DIV>
<DIV>Sent: Monday, June 23, 2014 9:05 PM </DIV>
<DIV>To: Green Building </DIV>
<DIV>Subject: Re: [Greenbuilding] Veneer Foam Panels </DIV>
<DIV> </DIV>
<DIV>The approach does solve the rather major thermal bridges of the floor 
penetrations throough the wall.  It does breaks the thermal bridge of the 
plates and studs though.</DIV>
<DIV>It places the main structure to the exterior, and hence exposes it wild 
swings in temp and RH with attendant movement and durability issues. Major 
problem with all interior insulation solutions.</DIV>
<DIV>I dont know what “drafting air” through the studs means but it does not 
sound like a good idea :)</DIV>
<DIV> </DIV>
<DIV>Which leads to the question, why would you try to do this? It is so easy to 
place the interior finish, veneer grade plywood, drywall, MDF, etc. on the 
interior of the studs of a normal high performance wood frame enclosure (see 
building science.com).  Why not do that?  It is easy to add EPS to the 
exterior of the framing, no gluing needed. This protects the framing from 
temperature and humidity swings. It allows the air -water barrier to be placed 
over the framing, and yet protects the air-water barrier from the worse 
temperature extremes, thereby adding longevity and reducing the risk of cold 
weather condensation.  All that is needed is to add furring strips screwed 
through the exterior insulation, otherwise almost everything is the same as 
normal construction.  And exterior insulation improves the durability and 
performance all round.</DIV>
<DIV> </DIV>
<DIV>John</DIV>
<DIV> </DIV>
<DIV>On Jun 23, 2014, at 7:34 PM, <conservationarchitect@rockbridge.net> 
<conservationarchitect@rockbridge.net> wrote:</DIV>
<DIV> </DIV>
<DIV>> I am interested in bonding a veneer grade plywood to a 4 to 6 inch 
thick panel of EPS foam that could be set to the interior of building framing to 
achieve a continuous thermal barrier.  I am wanting the beauty of the wood 
to replace the need for conventional sheetrock so this can be the finished 
surface.  I think that the thickness of the foam bonded to the plywood 
makes both more rigid and able to take some loading.  Although, unlike SIPs 
I want the main structure to be separate from the insulation (thermal 
barrier).  I am wondering if using low investment methods such as spreading 
foam appropriate panel adhesive over eps foam laid flat would achieve adequate 
bonding.  I am also wondering if humidity is a factor in bonding and or 
dimensional stability.  I would seal the seams. The seams would be covered 
with a finish grade wood strip.</DIV>
<DIV>>  </DIV>
<DIV>> If I had the structural sheathing (osb or plywood) to the interior 
side of conventional wood framing, siding could be mounted directly onto the 
framing to allow for drafting in the cavity which can serve as the drain dry 
plain that is needed if we are not drafting heated air through the wall.</DIV>
<DIV>>  </DIV>
<DIV>> The intention is to set these panels on the floor framing to be 
primarily self supporting avoiding the need for the long fasteners that drive up 
cost and likely reduce thermal performance.  In some cases, I would use the 
flat ceiling for the top of the thermal barrier.  I was interested in 
installing some exposed ceiling rafters that would be supported by a ledger 
mounted to the wall foam-plywood panels.  I would set veneer plywood above 
and support thick layer of foam.  The loads would be only the rafters, foam 
and the plywood.  Live load and dead loads from the main roof are carried 
by conventional wood trusses.  These ceiling rafters wedge the wall 
paneling in place.  This ceiling assembly can be set in place without 
bonding.  This also avoids the long fasteners.  I would top off the 
ceiling foam from the attic side with fire retarded cellulose to serve as the 15 
minute fire barrier required by code. </DIV>
<DIV>> _______________________________________________</DIV>
<DIV>> Greenbuilding mailing list</DIV>
<DIV>> to Send a Message to the list, use the email address</DIV>
<DIV>> Greenbuilding@bioenergylists.org</DIV>
<DIV>> </DIV>
<DIV>> to UNSUBSCRIBE or Change your List Settings use the web page</DIV>
<DIV>> 
http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</DIV>
<DIV> </DIV>
<DIV>John Straube</DIV>
<DIV>www.JohnStraube.com</DIV>
<DIV> </DIV>
<DIV> </DIV>
<DIV>_______________________________________________</DIV>
<DIV>Greenbuilding mailing list</DIV>
<DIV>to Send a Message to the list, use the email address</DIV>
<DIV>Greenbuilding@bioenergylists.org</DIV>
<DIV> </DIV>
<DIV>to UNSUBSCRIBE or Change your List Settings use the web page</DIV>
<DIV>http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org</DIV>
<DIV> </DIV></DIV></DIV></BODY></HTML>