<div dir="ltr">Lstiburek rocks. Thank you for that article, Jeff.<br></div><div class="gmail_extra"><br><div class="gmail_quote">On Sun, Dec 11, 2016 at 7:58 AM, Jeff Martin <span dir="ltr"><<a href="mailto:jeff@open2learn.ca" target="_blank">jeff@open2learn.ca</a>></span> wrote:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <p>Leslie,</p>
    <p>Adding an interior air barrier will almost certainly fix the
      obvious problem of condensation running out of the ceiling and
      down the walls, but it's still not great building science and,
      unless detailed meticulously, may not be enough to avoid future
      problems with moisture damage to the roof assembly. In addition to
      the great GBA article that you've linked to, you might want to
      check out this Joe Lstiburek article that appeared in Fine
      Homebuilding a few years ago, to get a better understanding of
      building science basics for roof ventilation:</p>
    <p><a class="m_-7808219107655715282moz-txt-link-freetext" href="https://buildingscience.com/sites/default/files/migrate/pdf/PA_Crash_Course_Roof_Venting_FHB.pdf" target="_blank">https://buildingscience.com/<wbr>sites/default/files/migrate/<wbr>pdf/PA_Crash_Course_Roof_<wbr>Venting_FHB.pdf</a></p>
    <p>If the chosen solution is to just try to achieve a better
      interior air seal, rather than a more robust (and expensive)
      solution of rebuilding the roof assembly so that it is either
      properly vented (soffit and ridge vents, with baffles the full
      length of the rafter bays) or uses a layer of impermeable
      insulation to provide the air sealing and prevent moisture
      build-up on the underside of the roof deck (e.g., 2 or 3 inches of
      closed-cell spray foam on the underside of the roof deck), the
      wood paneling will need to be removed from the ceiling and a good
      quality membrane carefully installed on the underside of the
      rafters, prior to reinstalling the t&g planks. Since you would
      be relying on this membrane to do all the work of keeping moist
      air away from the cold roof deck, I think you would want to use a
      really good membrane, like Pro Clima INTELLO Plus. CertainTeed's
      MemBrain is another option that's likely to cheaper and easier to
      source, but we've found that it's somewhat fragile. In any case,
      the membrane should installed using quality sealants and tapes,
      and as per manufacturer recommendations. When reinstalling the
      wood finish, care will need to be taken to minimize damage to the
      membrane. If there are too many breaches in your air barrier, they
      may lead to decay in the roof assembly that won't show up for
      years.</p>
    <p>That said, I think it would be more prudent to go for a more
      robust solution, if budget allows. Pulling the Roxul and adding an
      adequate layer of spray foam to the underside of the roof deck
      would probably be the cheapest and least labor-intensive solution,
      in this context. Considering your climate and the depth of the
      rafter bays, it appears that 2" of closed-cell spray foam would be
      adequate.</p><span class="HOEnZb"><font color="#888888">
    <p>Jeff<br>
    </p></font></span><div><div class="h5">
    <br>
    <div class="m_-7808219107655715282moz-cite-prefix">On 12/10/2016 9:20 PM, Leslie Moyer
      wrote:<br>
    </div>
    <blockquote type="cite">
      <div style="font-family:Arial,sans-serif;font-size:10pt">So it
        sounds like you're all pretty much in agreement that an air
        barrier will fix the problem.  It seems to me that they have NO
        air barrier now--good, bad or otherwise.  I.e. they don't have
        penetrations in their air barrier--they don't HAVE an air
        barrier.  The layers in the roof/ceiling assembly my friend
        describes below are the ENTIRETY of the construction....he
        listed everything in order as it is. As far as vapor movement
        goes, they are aware that the Roxul is not a vapor barrier and
        neither is the tongue and groove ceiling. <span style="font-size:10pt">I was leaning toward a "thermal
          bridging" problem & thought rigid foam insulation would
          fix it...either under the boxcar siding or under the roof
          sheathing. </span>
        <div><span style="font-size:10pt"><br>
          </span></div>
        <div><span style="font-size:10pt">There are no can lights in
            the ceiling.  There is wiring in place for one fixture, I
            believe, but no other large holes.  I'm not sure, but I
            don't think they have drywall under the tongue and groove
            boxcar siding on the ceiling--he didn't mention it below and
            he didn't mention it in his conversation with me earlier
            today.</span>
          <div>
            <div><br>
            </div>
            <div>This is a brand new addition--unfinished still--and
              they are not looking for a short-term fix. The builder
              just left and is willing to come back to fix the problem
              now, but they need to come to an agreement about what that
              "fix" will entail.  <br>
              <div><br>
              </div>
              <div>So, for a solution, they need to air seal all holes
                of any size that go from the sidewall plates up into the
                ceiling; air-seal all holes that penetrate into the
                ceiling. Where, exactly, should the air barrier be
                installed?  "The warm side" doesn't tell me
                enough--there are several layers on the warm side.  They
                need to know if they should approach this by removing
                the metal roofing & sheathing and go in from the
                top, or remove the tongue and groove siding on the
                ceiling and fix things from the inside-out.  </div>
              <div><br>
                -Leslie Moyer<br>
                <br>
                --- <a class="m_-7808219107655715282moz-txt-link-abbreviated" href="mailto:obrien@hevanet.com" target="_blank">obrien@hevanet.com</a> wrote:<br>
                <br>
                From: "Michael O'Brien" <a class="m_-7808219107655715282moz-txt-link-rfc2396E" href="mailto:obrien@hevanet.com" target="_blank"><obrien@hevanet.com></a><br>
                To: Green Building
                <a class="m_-7808219107655715282moz-txt-link-rfc2396E" href="mailto:greenbuilding@lists.bioenergylists.org" target="_blank"><greenbuilding@lists.<wbr>bioenergylists.org></a><br>
                Subject: Re: [Greenbuilding] Unvented cathedral ceiling
                condensation<br>
                Date: Sat, 10 Dec 2016 13:38:28 -0800<br>
                <br>
                Hi, Leslie—
                <div><br>
                </div>
                <div>Just wanted to chime in to agree about the air
                  leaks across the interior side of the cathedral
                  ceiling. Not only recessed can fixtures, but often
                  every wiring hole drilled through top plates, every
                  vent stack and flue have not been sealed to block air
                  leaks. The walls may be contributing, too, if there
                  are penetrations in the top plates. </div>
                <div><br>
                </div>
                <div>The long-term fix is to take down the ceiling
                  drywall so the leaks can be sealed and a proper vapor
                  rertarder installed, but in the short term they could
                  run a dehumidifier to reduce the water vapor in their
                  occupied space. </div>
                <div><br>
                </div>
                <div>Sometimes builders will open up the blocks along
                  the eaves and install some sort of vent at or near the
                  ridge, but this may have the effect of sending cold
                  air under the insulation and cooling down the interior
                  surface of the ceiling, it takes some detailing to
                  keep the vent air above the insulation.</div>
                <div><br>
                </div>
                <div>Best wishes,</div>
                <div><br>
                </div>
                <div>Mike O’Brien</div>
                <div><br>
                </div>
                <div><br>
                </div>
                <div><br>
                  <div>
                    <div>On Dec 10, 2016, at 11:50 AM, Leslie Moyer <<a href="mailto:unschooler@lrec.org" target="_blank">unschooler@lrec.org</a>>
                      wrote:</div>
                    <br>
                    <div>
                      <div style="font-family:Arial,sans-serif;font-size:10pt">
                        <div><span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">I have some nearby
                            friends having a problem. I think I
                            understand what the problem is, and even
                            some possible ways to solve it, but I'm not
                            certain I could give them advice that would
                            fix their problem the best or cheapest way.
                            I thought you guys could, though!  </span></div>
                        <div><span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)"><br>
                          </span></div>
                        <div><span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">They read this article
                            & I think they will go ahead and pay to
                            read the article referenced within it: </span></div>
                        <div><span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)"><br>
                          </span></div>
                        <span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">
                          <div><a href="http://www.greenbuildingadvisor.com/blogs/dept/musings/how-build-insulated-cathedral-ceiling" target="_blank">http://www.<wbr>greenbuildingadvisor.com/<wbr>blogs/dept/musings/how-build-<wbr>insulated-cathedral-ceiling</a></div>
                          <div><br>
                          </div>
                          <div>We are considered a "hot humid"
                            climate--NE Oklahoma </div>
                          …………………………….</span><br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">We have a question regarding
                          condensation problems in a cathedral ceiling. 
                          We live in northeastern Oklahoma (zone 3) and
                          just added a dinning room (cathedral ceiling)
                          15 x 19 addition.  The addition was just
                          opened up to the main house earlier this week,
                          and we got hit with (what are for us) very
                          cold temperatures.  Thursday night had a low
                          of 12 F.  By noon on Friday we noticed that
                          water was dripping down the north side
                          interior wall  (along the drywall).  The drip
                          lines appeared to be spaced every 24 inches,
                          or about where a roof rafter would be.</span><br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">The ceiling/roof construction was
                          constructed with 2 x 8 rafters and insulated
                          with R30 Roxul (rock wool) insulation and is
                          not vented.  The interior ceiling is wooden
                          tongue and groove car siding.   The roof
                          decking is LP TechShield Radiant Barrier (with
                          the metal foil side facing the interior of the
                          house, as described on the boards) with a
                          metal roof (there is felt paper in between the
                          decking and the metal roof on the North side,
                          but on the South side we used double bubble). 
                           We did not have any condensation issues on
                          the south wall.</span><br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <br style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px">
                        <span style="color:rgb(49,49,49);font-family:Roboto;font-size:16px;word-spacing:1px;background-color:rgb(255,255,255)">We have spoken with over half a
                          dozen different experts, and we’re getting as
                          many different suggested solutions.  We are
                          desperate to fix this problem and would
                          greatly appreciate any help!  Thank you!</span></div>
                      ______________________________<wbr>_________________<br>
                      Greenbuilding mailing list<br>
                      to Send a Message to the list, use the email
                      address<br>
                      <a href="mailto:Greenbuilding@bioenergylists.org" target="_blank">Greenbuilding@bioenergylists.<wbr>org</a><br>
                      <br>
                      to UNSUBSCRIBE or Change your List Settings use
                      the web page<br>
<a class="m_-7808219107655715282moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" target="_blank">http://lists.bioenergylists.<wbr>org/mailman/listinfo/<wbr>greenbuilding_lists.<wbr>bioenergylists.org</a></div>
                  </div>
                  <br>
                </div>
                ______________________________<wbr>_________________
                Greenbuilding mailing list
                to Send a Message to the list, use the email address
                <a href="http:///eonapps/ft/wm/page/compose?send_to=Greenbuilding%40bioenergylists.org" target="_blank">Greenbuilding@bioenergylists.<wbr>org</a>
                to UNSUBSCRIBE or Change your List Settings use the web
                page
                <a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" target="_blank">http://lists.bioenergylists.<wbr>org/mailman/listinfo/<wbr>greenbuilding_lists.<wbr>bioenergylists.org</a></div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="m_-7808219107655715282mimeAttachmentHeader"></fieldset>
      <br>
      <pre>______________________________<wbr>_________________
Greenbuilding mailing list
to Send a Message to the list, use the email address
<a class="m_-7808219107655715282moz-txt-link-abbreviated" href="mailto:Greenbuilding@bioenergylists.org" target="_blank">Greenbuilding@bioenergylists.<wbr>org</a>

to UNSUBSCRIBE or Change your List Settings use the web page
<a class="m_-7808219107655715282moz-txt-link-freetext" href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" target="_blank">http://lists.bioenergylists.<wbr>org/mailman/listinfo/<wbr>greenbuilding_lists.<wbr>bioenergylists.org</a></pre>
    </blockquote>
    <br>
  </div></div></div>

<br>______________________________<wbr>_________________<br>
Greenbuilding mailing list<br>
to Send a Message to the list, use the email address<br>
<a href="mailto:Greenbuilding@bioenergylists.org">Greenbuilding@bioenergylists.<wbr>org</a><br>
<br>
to UNSUBSCRIBE or Change your List Settings use the web page<br>
<a href="http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org" rel="noreferrer" target="_blank">http://lists.bioenergylists.<wbr>org/mailman/listinfo/<wbr>greenbuilding_lists.<wbr>bioenergylists.org</a><br></blockquote></div><br></div>