[Greenbuilding] Weight of spray cellulose
Topher Belknap
topher at greenfret.com
Mon Feb 20 11:24:25 CST 2017
Greetings,
What is the permeability of the spray foam? If it is low, you will need
to ensure drying to the inside, which seems problematic. Have you run a
WUFI simulation, or similar?
Thank you kindly,
Topher
--
Topher Belknap
Green Fret Consulting
Kermit didn't know the half of it...
http://www.GreenFret.com/
(207) 882-7652
On 2/19/2017 11:24 PM, Sacie Lambertson wrote:
> We're in Zone 4. We will put in several inches of sprayed foam
> immediately under the roof; sealed to the tops of existing walls. Blown
> in cellulose is the next layer. Area/attic is _not_ ventilated. The
> house will be tight.
>
> Will have an HRV system as well.
>
> Should have described whole plan to begin with. Again, appreciate the
> comments.
>
> Sacie
>
> On Sun, Feb 19, 2017 at 9:16 PM, John Straube <jfstraube at uwaterloo.ca
> <mailto:jfstraube at uwaterloo.ca>> wrote:
>
> There are numerous reasons to ventilate attics and cathedral
> ceilings: removal of moisture is the most important.
> Another reason is to limit ice damming in climates with sufficient
> snow and weather that cycles near to freezing temperatures. If you
> insulate enough, you dont need to ventilate for that reason.
> BUT, there is no way you can build cathedral ceilings with cellulose
> and NOT ventilate without taking serious risks. Some cellulose
> companies have been selling this idea for years, and we (and most
> other forensic consultants) have seen sufficient failures to realize
> that it is too risky in most cases. If the house below is super air
> leaky and hence very dry in cold weather you can often “get away
> with it” but modern houses in cold climates with higher RH levels
> (e.g. not 15%!) cannot tolerate small air leaks.
> Do a great job of air sealing, live in a climate that is not too
> cold (e.g. Zone 3 or 4) and you might be able to pull off a
> cellulose unvented cathedral. Still risky, but must less so.
> An alternate design is to put enough insulation outboard of the
> sheathing and cellulose. This is a good retrofit option. Fill up the
> available rafter space, then put an air barrier membrane on the
> sheathing, and add sufficient R-value on the exterior to avoid
> condensation (this amount varies ratiometrically with the amount of
> cellulose R-value, the outdoor climate, and the indoor winter humidity.
>
> PS I have R-100 in my house… roughly. about 28” of cellulose in a
> flat ceiling under a well-ventilated attic. No furring, just 2x4
> bottom chords of trusses supporting 1/2” GWB with standard screw
> patterns. R-100 does not make a lot of sense, until you see the
> price difference between R-60 and R-100 is so small
> But Frank’s experience is worth a lot…. 30 houses over more than a
> decade. That is worth more than any experiment in my books.
>
>
> > On Feb 19, 2017, at 9:32 PM, Reuben Deumling <9watts at gmail.com
> <mailto:9watts at gmail.com>> wrote:
> >
> > R80, huh? Wow.
> > I'm curious, Frank, what you make of the article circulated here
> recently that suggested that (and I'm paraphrasing) above R30 the
> ventilation of cathedral ceilings could be skipped?
> >
> > On Sun, Feb 19, 2017 at 6:05 PM, Frank Tettemer
> <frank at livingsol.com <mailto:frank at livingsol.com>> wrote:
> > I agree with David's suggestion, to alleviate concern,
> > However, for over a decde we have in 22 inches of blown in place
> cellulose = (R-80?). this had held up consistantly each year, We put
> up MemBrain by Certainteed stapled to the ceiling joists @ 24" o.c..
> > Then, 1x4 spruce strapping on 12" o.c.
> >
> > Then 1/2" drywall, double screwes into 1x4 on 9" o.c..
> >
> > At least 30 ceilings and insulation installations over 14 years,
> > with no failures except in my own garage ceiling where I stepped
> off the joists with my big bad foot.
> >
> > Question?: Do you have a plan to block off the vented soffits, and
> allow ventilation channels from the vented soffit, above the
> cellulose, to the vented ridge, or, maximum vent box, or similar?
> > More opportunities and good use of corrugated cardboard?
> > Or inexpensive Moore vent/rafter vents, and vertical cardboad
> baffles, from outside face of the wall plate, up to the rafter vents?
> >
> > Cheers,
> > Frank Tettemer
> >
> > On 2017-02-18 12:29 PM, David Wentling via Greenbuilding wrote:
> > _______________________________________________
> > Greenbuilding mailing list
> > to Send a Message to the list, use the email address
> > Greenbuilding at bioenergylists.org
> <mailto:Greenbuilding at bioenergylists.org>
> >
> > to UNSUBSCRIBE or Change your List Settings use the web page
> >
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
> >
> >
> > _______________________________________________
> > Greenbuilding mailing list
> > to Send a Message to the list, use the email address
> > Greenbuilding at bioenergylists.org
> <mailto:Greenbuilding at bioenergylists.org>
> >
> > to UNSUBSCRIBE or Change your List Settings use the web page
> >
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
> >
> > _______________________________________________
> > Greenbuilding mailing list
> > to Send a Message to the list, use the email address
> > Greenbuilding at bioenergylists.org
> <mailto:Greenbuilding at bioenergylists.org>
> >
> > to UNSUBSCRIBE or Change your List Settings use the web page
> >
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>
> Dr John F Straube, P.Eng.
> jfstraube at uwaterloo.ca <mailto:jfstraube at uwaterloo.ca>
> www.JohnStraube.com <http://www.JohnStraube.com>
>
>
>
>
> _______________________________________________
> Greenbuilding mailing list
> to Send a Message to the list, use the email address
> Greenbuilding at bioenergylists.org
> <mailto:Greenbuilding at bioenergylists.org>
>
> to UNSUBSCRIBE or Change your List Settings use the web page
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
> <http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org>
>
>
>
>
> _______________________________________________
> Greenbuilding mailing list
> to Send a Message to the list, use the email address
> Greenbuilding at bioenergylists.org
>
> to UNSUBSCRIBE or Change your List Settings use the web page
> http://lists.bioenergylists.org/mailman/listinfo/greenbuilding_lists.bioenergylists.org
>