Alan Abrams <alan at abramsdesignbuild.com> wrote:
> I came across a claim that a 12" thick AAC block wall achieves R-22 (more than double the rated per unit R-value of the material itself) in the Washington, DC climate... I am skeptical of the claim mentioned above, and would not want to count on it for the not unusual three weeks of late January when the daytime temp never gets out of the 20's... am I alone?
No. This works best when the outdoor highs and lows are less than and greater than 68 F...
On a day with average exterior temp T, a 68 F concrete
house with 2" R10 Styrofoam walls will lose or gain about |68-T|/R10 Btu/h.
With min and max temps Tmin and Tmax, a frame house in the same location
with walls with an equivalent R-value might lose (68-Tmin)/R all night and
gain (Tmax-68)/R all day, with an equivalent R-value of 5(Tmax-Tmin)/|68-T|.
Here is a list of US locations and equivalent R-values, based on NREL data:
location month Tmin T Tmax equivalent R-value
Philadelphia June 61.8 71.8 81.7 26.2
Phoenix, AZ April 55.3 69.9 84.5 76.8
Flagstaff July 50.5 66.3 81.9 92.3
Prescott June 49.9 67.2 84.5 216.3
Albuquerque September 55.2 68.6 81.9 222.5
San Diego October 60.9 67.7 74.6 228.3
Houston April 58.1 68.3 78.4 338.3
Ely, NV July 48.0 67.5 87.0 390.0
Colorado Springs August 55.2 68.3 81.3 435.0
Las Vegas October 54.3 68.3 82.1 463.3
Elkins, WV August 56.2 67.8 79.3 577.5
Bakersfield October 54.8 67.8 80.7 647.5
Rock Springs, WY July 52.8 68.0 83.1 infinite!